8.5kw shower on a 32amp mcb | on ElectriciansForums
Discuss 8.5kw shower on a 32amp mcb in the UK Electrical Forum area at ElectriciansForums.net
Hello All
Can any one provide non sarcastic suggestions as to why an 8.5kw shower has not tripped the 32amp mcb protecting that circuit?
Found this install in a domestic property. It seems to have been there for years, without out issue.
DD
Im just dealing with something similar.
8.5kW on a 30A breaker. This one is actually tripping it, but only if the temperature is high and they spend too long in there.
As in the first post, have a look at appendix 3, page 370 of the new edition of BS7671 and you will see that it is highly unlikely a 32A breaker will trip with a 8.5kW shower (approx 37A-no calculator to hand).
If it's a B type it would need to get to about 46amps before it started to think about tripping.
8.5 kW @230v is about 37A.
See page 370. BBB
Remember a B type breaker only needs to disconnect within .4 seconds at 5 times it's rated current
Reply to 8.5kw shower on a 32amp mcb in the UK Electrical Forum area at ElectriciansForums.net
Duh!!! Just re-read Op's original post, it was converted to a RFC!
J