Hello, I've read a few similar threads online but none come up with an answer.
I recentally replaced a 7.2 Kw shower with a Triton 8.5 Kw shower. But trips the mcb after of running the shower for 20 minutes.
While installing the shower I replaced the 6mm with 10mm T&E, and the 50 amp pull cord Isolator.
The cable runs 50% conduit 50% open air. 9 meter cable run
MCB Wylex 45amp
The cable stay's cool while running but the mcb gets very hot
Clamp meter reads 35.1amps.
and checked for any loose connections