Just arrived at a job, 45amp shower isolator completely burnt out.
Checked cable and it's 4mm tne in trunking to 8.5kw triton riba shower on a 32amp mcb. Cable run is 5meters.
This was a new circuit installed only a few months ago. I expect loose connection on isolator causing burnt terminals.
I am going to request cable uprated to 6mm, anyone else make any sense why a 4mm was used?