just been to a job , saw that the shower 9.5 kw is on 6mm t&e the cable goes in the wall and under floor boards ,No insulation, to the board (A cable run of no more than 10 m) . I said downgrade the shower to 8.5 max. Is it really necessary ? never quite sure , its borderline to me .
 
i think thats right, its bang on the limit. but i would be ok with it if it seems to be holding up. keep it on the 40 and tell them they are pushing there luck. whatever happend to the super 7 shower ??? 10.5 kw crazy !!!
 
And the other little addition is, it may well be on the limit on a 40A, but 1.13 x 40 is over 45A......

I've seen a 6mm2 cable melting on a 10.8kW shower, again as prev poster mentions where it connects at the neutral bar. Always wonder if it was a loose conn (can't tell when all melted).
 
I also doubt that they will be having the shower running at full whack, not unless they have skin like leather.

Honestly don't understand these shower unit being 9.5 TO 10.5KW, The shower unit that i currently have in China is 4.2 or 4.6KW (do they do this sort of rating size in the UK??) and i can't have the thermostat turned up more than half way.

So what's the story with these Mega Watt shower units that seem to abound in the UK?? ...lol!!!

Yeah but doesn't China run at 650 Volts :chinese:
 
I see the good old 9.5kw shower on 6mm conundrum is still rumbling on after 4 pages lol.
Not in the least bit surprised
Anyways im off for a shower now , 8.5kw wired in 4mm if anyones interested.
If im not back assume the worst
:)
 
Last edited by a moderator:
It's no good people shouting about how a cable should be ok because the shower "should" only on for 10 mins. It's either suitable for the OCPD or it's not for goodness sake.
Really can't see what the argument is.
 
I was always of the understanding, the higher the kw rating of the shower, doesn't mean it gets hotter, just allows more water to flow at the required temperature.
The lower the power rating the less amount of energy it has to heat the water so it flows slower to maintain the temperature.
 
remember a few years back one of the sheds was doing 10.5kw showers for about £45 well a bloke fitted one on 6mm replacing his old 7.5kw cable ran on outside wall of house and it melted it from one end to the other,guy was well peed off.asked for a price and said the cost of cable alone was more than cost of shower,got quite funny about it so I told him that my shower worked fine so either way it didnt bother me if he had it fixed or not.lol
 
remember a few years back one of the sheds was doing 10.5kw showers for about £45 well a bloke fitted one on 6mm replacing his old 7.5kw cable ran on outside wall of house and it melted it from one end to the other,guy was well peed off.asked for a price and said the cost of cable alone was more than cost of shower,got quite funny about it so I told him that my shower worked fine so either way it didnt bother me if he had it fixed or not.lol

Nice answer haha. Not your fault his DIY went belly up!
 
I was always of the understanding, the higher the kw rating of the shower, doesn't mean it gets hotter, just allows more water to flow at the required temperature.
The lower the power rating the less amount of energy it has to heat the water so it flows slower to maintain the temperature.


Indeed mate, higher rating means better flow as power is fixed and temp is controlled by throttling water flow. Downside of a lower rated shower is on a winters morning when the water entering the unit isn't much above freezing... :christmaswindow:
 

Reply to 9.5 kw shower on 6mm ? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
328
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
306
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
366

Similar threads

  • Question
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Replies
5
Views
2K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
550

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top