9.5kw electric shower | on ElectriciansForums
Discuss 9.5kw electric shower in the UK Electrical Forum area at ElectriciansForums.net
Edij
West Drayton
Hi ,
I'm getting electrician to change my consumer unit and was planning to get :
it has 2 x 80a 30ma Type A RCD's
but for shower it says -
500 (9.5kW)41.345A10mm2RCBO
will this 80a fuse not be like overload or something? Do i need to buy 40-45A fuse?
An RCD is not a 'fuse'. 80A is its maximum load, and the sum of the MCBs running from it must not add up to more than 80A, unless your DNO fuse is 80A or less.
Following on from another thread I've just posted on, is the shower rated at 9.5kW @ 240V or 230V?
Shower info - A Power Input of 240 V and 40 amp circuit breaker is required for max output ( 9.5 KW )
in simple words ,if i buy that consumer unit ,will i need to buy any extra wylex fuses or what is there included is good enough?
The standard UK voltage is 230V, not 240V, so your shower is rated at 8.275kW in reality. The 9.5kW is marketing.
The current drawn by this will be around 36A, so yes, you do need to buy a 40A breaker AND, the sum of the breakers on the side of the CU you fit this must not add up to more than 80A, unless you can confirm that your DNO fuse is not more than 80A.
ok got it! so something like this?will this be compatible with that consumer unit?
Why is your electrician not specifying what board and protective devices you need?
Is diversity not taken into account?
Not any more.
According to the BEAMA guide that somebody posted the other day, it is. We never fit split load boards but according to this documant diversity IS taken into account when selecting and erecting.
If you have more upto date info can you share please?
I'm now retired from active contracting, so do not posses a copy of the 18th, although I try to keep up to date with changes from the 17th.
My information comes from recent previous posts on here, and as I understand it, it's a recent change.
Reply to 9.5kw electric shower in the UK Electrical Forum area at ElectriciansForums.net
With what looks like only 5 circuits you can probably put a little 5 way garage consumer unit in there if money is tight