Hi ,

I'm getting electrician to change my consumer unit and was planning to get :

it has 2 x 80a 30ma Type A RCD's

but for shower it says -
500 (9.5kW)41.345A10mm2RCBO

will this 80a fuse not be like overload or something? Do i need to buy 40-45A fuse?
 
According to the BEAMA guide that somebody posted the other day, it is. We never fit split load boards but according to this documant diversity IS taken into account when selecting and erecting.

If you have more upto date info can you share please?
Hi. It was me that posted the BEAMA document.
Apparently there is a 2 stage process when applying diversity to a group of circuits protected by an RCD.
Stage 1 work out and apply diversity.
Stage 2 read manufacturers literature.

Excerpt from BEAMA document:

"Conclusion
The minimum rated current Inc of the circuit in the consumer unit for the RCCB
(A) based upon diversity is 78.4 A. However, overload protection shall not solely be
based on the use of diversity factors of the downstream circuits, see Regulation
536.4.202. To achieve overload protection of the RCCB circuit, the rated current of
the OCPD shall be selected according to the manufacturer’s instructions
, which for
BEAMA members, is coordinating with the upstream OCPD, in this case a 100 A fuse.
Therefore, the required minimum rated current Inc in the circuit of the consumer unit for the
RCCB (A) is 100 A."


So, overall, not much point in calculating the diversity?
 

Reply to 9.5kw electric shower in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
270
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
771

Similar threads

  • Question
With what looks like only 5 circuits you can probably put a little 5 way garage consumer unit in there if money is tight
2
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top