Hi, While carrying out a periodic inspection I came across a 9kw shower on 4mm cable, 40A type B ocpd, 30ma rcd.
I have given a code 3, for the following reasons;
1. No sign of thermal damage at any termination.
2. Shower cannot overload as fixed load.
3. Short Circuit & Earth loop impedance well within limits.
4. Shower will not run at maximum 9kw.
I have also noted to the customer that the manufacturers recommend a 10mm cable. I would just like your opinions on the above.
Cheers