J
Jabbajaws
This may sound rather a strange question but its something that l need to understand. If a ring circuit, through a fault condition, or even by poor design, ended up becoming two radial circuits on a 32A MCB protected circuit, is there an actual danger present?
Although l know that this is not permitted in BS7671, im not sure of the reason why. Can anyone explain if this is actually dangerous, or if it is something that merely isn't permitted by the regs. Wouldn't the protective device still operate?
Thanks, Jabbajaws :cool:
Hi.
Simple reason being that a 2.5mmT+E is not able to carry 32A as a radial. Depending on where you look and with regard to various factors etc it's around 27A
Check out the CCC tables in BS7671. A 2.5mm should never be on anything more than a 20A radial.
just asthe guys above say, it's all down to the current rating of the cable.
Kind of going off topic here, but i remember a few years ago hearing that Ringmains were going to be phased out due to this problem??? anyone else heard the same.
(It could just have been me having a strange dream of course:D )
I did my 17th a couple of weeks ago and got told the same.
All down to cenelec I'm afraid..
On the subject of a broken ring, apart from the high cpd for 2.5mm t&e, what about the dangers of
live conductors where the fault is...
Further investigation would be required, as this situation is not acceptable.
It doesn't take a brain surgeon to find, even though it may take time, but once found can be rectified.