This may sound rather a strange question but its something that l need to understand. If a ring circuit, through a fault condition, or even by poor design, ended up becoming two radial circuits on a 32A MCB protected circuit, is there an actual danger present?

Although l know that this is not permitted in BS7671, im not sure of the reason why. Can anyone explain if this is actually dangerous, or if it is something that merely isn't permitted by the regs. Wouldn't the protective device still operate?

Thanks, Jabbajaws :cool:
 
Hi.

Simple reason being that a 2.5mmT+E is not able to carry 32A as a radial. Depending on where you look and with regard to various factors etc it's around 27A

Check out the CCC tables in BS7671. A 2.5mm should never be on anything more than a 20A radial.
 
just asthe guys above say, it's all down to the current rating of the cable.

Kind of going off topic here, but i remember a few years ago hearing that Ringmains were going to be phased out due to this problem??? anyone else heard the same.

(It could just have been me having a strange dream of course:D )
 
just asthe guys above say, it's all down to the current rating of the cable.

Kind of going off topic here, but i remember a few years ago hearing that Ringmains were going to be phased out due to this problem??? anyone else heard the same.

(It could just have been me having a strange dream of course:D )

I did my 17th a couple of weeks ago and got told the same.
 
All down to cenelec I'm afraid..

On the subject of a broken ring, apart from the high cpd for 2.5mm t&e, what about the dangers of

live conductors where the fault is...

Further investigation would be required, as this situation is not acceptable.

It doesn't take a brain surgeon to find, even though it may take time, but once found can be rectified.

:eek:
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
A Broken Ring!!!
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
9
Unsolved
--

Advert

Thread statistics

Created
Jabbajaws,
Last reply from
Jabbajaws,
Replies
9
Views
2,020

Advert

Back
Top