Three core SWA installed as a new circuit on a TNS supply. Both ends of the SWA are earthed.
Would you/ is it acceptable to include the armour in the R1+R2 calculation (ie in parallel with the core being used as cpc) or should measurement simply be between cores?
 
Sorry you don’t think I am being real.
Sidestep what?
I think what you should really be asking, is what to do if conduit or trunking is used as a CPC.
Why should I be asking it? No problem, as far as I'm concerned....or the regs.
I'm sure I wouldn't use cable tray as a cpc, though. Unlike an swa, the wiring's not fully contained.
 
GN8 states (for an SWA with inadequate armour csa to be used as a cpc) that where the armour is earthed and there is also an internal core used as the cpc that the current division between the two parallel conductors cannot be determined and so the separate core should be sized as a stand alone conductor.

Therefore when measuring R1+R2 the armour should not form part of the resistance measurement as the internal core must meet the requirements on its own. Obviously the armour will lower the resistance and presumably assist disconnection but cannot be relied upon.
 
At last Richard, the answer! :)
In the particular case which prompted the op, the SWA armour, the equivalent csa would have allowed it to be used as the cpc, but with the third core present, not required to.
 

Reply to A daft question, or not....! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
382
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
963
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
It's the same with any system, if you put poo in, you get poo out!
Replies
4
Views
2K
  • Question
Just re-read the OP's post and it is an existing 5C SWA so presumably a 3P supply. For 40A and 150m you are seeing 6.6V drop or 1.65% of 400V 3P...
Replies
8
Views
893

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top