L

lee1002

hi im doing my 2391 in a couple of weeks and i have just been going through a few past papers i have. Im just a little unsure about these questions and wondered if anyone could help me.

1) state why the test for continuity of protective conductors must be conducted before:
a)insulation resistance
b)polarity
c)earth fault loop impedance
I know that it will be needed to be done to show there is an earth fault path but unsure on the rest.

2)state
a)the two ip codes relating to penetration tests on enclosures that have had insulation applied on site.
b) which other tests should be applied to a)

thanks.
 
An insulation test could be carried out at the extremity of a circuit where the cpc is not continuous
You would then be insulation testing live/neutral to nothing

You need cpc continuity confirmed, before the result of an insulation test can be asured for that reason
 
hi im doing my 2391 in a couple of weeks and i have just been going through a few past papers i have. Im just a little unsure about these questions and wondered if anyone could help me.

2)state
a)the two ip codes relating to penetration tests on enclosures that have had insulation applied on site.
b) which other tests should be applied to a)

thanks.

Not certain but is this to do with horizontal up facing surface on CU which must be IPX4 (use blind grommets and push canbles through) and all othe surfaces needing to to be IPX2 (use open grommets)

It is to stop the risk of falling strands of wire entering the CU. Not sure what it is getting at with part b) so i could be wrong.

With the continuity - insulation resistance test (in addition to what Des said) you need to ensure that your IR test is over the whole length of all conductors
. If you hadn't already proved continuity you wouldn't know this.
 
im not sure about part b either m8 i have just bought the gn3 so going to have alook through it and see what it says in there. thanks for your help
 

Reply to A few questions in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
787

Similar threads

  • Question
He is after the four options for 1 and 2 of the multiple choice exam, probably optimistic someone will know this. Your question 3 in incomplete to...
Replies
2
Views
1K
  • Question
There is no homework, and I'll never see these photo again.
Replies
3
Views
603

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top