a freind buying house this is pereodic report he has I have taken a snip only | on ElectriciansForums

Discuss a freind buying house this is pereodic report he has I have taken a snip only in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Various details missing there, which should not be missing IMO. Namely end to end values on some circuits and R1R2 values. Limitations to the testing is acceptable, but in this instance some important potential issues have not been either deduced or verified to be OK.

I have never completed a inspection and test of a installation without at least one observation being made (in reference to the second picture). Was there a page before the second photo that had any observations perhaps.

Who did the testing - a small or large company or one man band? And of of curiosity how much was paid.

Oh, and the Zs values should be recorded too. Poor.
 
Last edited:
5 sec. disconnection time for lights, 0.4 secs. for circuits > 32A. what a plonker.
 
Hello All

local sparks to me, full contractor, this is from the solicitor to my friend buying the house, I said not worth paper written on, he contacted estate agent they mentioned it says satisfactory & client of theirs have paid for the test.
I am now going in Monday to do periodic for property.

I did not show the rest but least I say we have TNCS down but with a figure 0.80 for the ze inquired so says it all
 
5 bed house, not saying impossible but 200M ohms L/N IR testing find hard to believe myself but we shall see I will post up my results when I have done
 
Last edited:
That's some bad testing I bet the actual results are nothing like that haha.

Got to love this types of testing, worked for a company before (only as a trainee so working with a sparky) when doing DB upgrades who said just do a Ze and a Zs on sockets and rcd test that's it the supervisor in office will fill in the rest. also if there is a link between lighting which causes rcd to trip just put both lighting on same rcd not even try to find the problem. Safe to say I wasn't there long.
 
testing the above house start of the results just writing up now, just got to edit parts of cert fill in the new blanks have some other pictures will try & post.
also observations page
 

Reply to a freind buying house this is pereodic report he has I have taken a snip only in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
395
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
980
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Has the cover been removed, is it TP bussbar? I fitted one as @oscar21 linked to a few months ago, it was actually a nice board and with the TP...
Replies
5
Views
653
Twin and earth on its own isnt going to meet the requirements for burial. Why not use Swa ?
Replies
1
Views
300

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top