Hi guys,
I have been doing a bit of testing today and need a liitle input if possible. The installation is TN-S at source. There is a 50A switchfuse which feeds two distribution boards in a B & B outbuilding. The supply comes into the first D.B (in one of the B & B rooms) into the top of an upfront RCD (30mA) and then feeds the next D.B ( in the other B & B room). This also has an RCD (30mA) up front. The first D.B has been TT'd which is brilliant and has the supply earth segregated. However the earth from the second D.B has its earth from the first D.B earth bar instead of it's own earth stake.
As it stands, any RCD testing on the first D.B results in the second D.B's RCD tripping. Not ideal. But my main concern is the cpc that feeds the second D.B is an inadequate size. It is 4mm (10mm T+E). Ideally, they should have TT'd this D.B aswell. Unfortunately (as ever) it has all been plastered and finished long ago.
Potential soulutions:
1: TT the second D.B and segregate the incoming cpc feed. The downside is surface cabling to achieve this.
2: Could i get away with feeding the second D.B off the first D.B via an MCB? I would change the second D.B to a main switch up front. PFC for the second D.B is 0.434kA and measured Ze is 3.57 Ohms. I calculated the adiabatic equation using a disconnection time of 0.2s. The result is 1.68mm ( i think!) Would this be acceptable! Obviously, any earth fault in the second D.B would result in the RCD tripping both rooms out! Not ideal!
Any input would be greatly appreciated!
Thanks in anticipation,
Dave
I have been doing a bit of testing today and need a liitle input if possible. The installation is TN-S at source. There is a 50A switchfuse which feeds two distribution boards in a B & B outbuilding. The supply comes into the first D.B (in one of the B & B rooms) into the top of an upfront RCD (30mA) and then feeds the next D.B ( in the other B & B room). This also has an RCD (30mA) up front. The first D.B has been TT'd which is brilliant and has the supply earth segregated. However the earth from the second D.B has its earth from the first D.B earth bar instead of it's own earth stake.
As it stands, any RCD testing on the first D.B results in the second D.B's RCD tripping. Not ideal. But my main concern is the cpc that feeds the second D.B is an inadequate size. It is 4mm (10mm T+E). Ideally, they should have TT'd this D.B aswell. Unfortunately (as ever) it has all been plastered and finished long ago.
Potential soulutions:
1: TT the second D.B and segregate the incoming cpc feed. The downside is surface cabling to achieve this.
2: Could i get away with feeding the second D.B off the first D.B via an MCB? I would change the second D.B to a main switch up front. PFC for the second D.B is 0.434kA and measured Ze is 3.57 Ohms. I calculated the adiabatic equation using a disconnection time of 0.2s. The result is 1.68mm ( i think!) Would this be acceptable! Obviously, any earth fault in the second D.B would result in the RCD tripping both rooms out! Not ideal!
Any input would be greatly appreciated!
Thanks in anticipation,
Dave