Just received a couple of Electrical Danger Notifications (C2's) from our annual electrical inspections.

"No co-ordination between conductor and protective device cct 1T/P 2.5mm - 32A ref method B"

&

"High values of measured EFLI at ccts 6TP-15TP"

Could you offer some advice as to what these mean, as I'd like to have some understanding before I talk to our electrical contractor.

Thank you in advance.
 
1 seems like an undersized earth conductor (cpc). it's a bit vague

2 is a high reading of the earth fault path on several circuits.
 
The person issuing the report should be explaining any issues so they are understood by the customer. Ask for clarification.

Issue 1 is saying that the cable used for the circuit is too small for the circuit breaker and vice versa. Simplest fix is to change the breaker size if the connected load will allow.

Issue 2 is saying the earth fault path of several circuits is not sufficient. Extra or larger earth conductors could be added or the size of circuit breakers reduced again if loads will allow.
 
Last edited:
The person issuing the report should be explaining any issues so they are understood by the customer. Ask for clarification.

Thank you for your reply Andy. I agree there should have been more information or at least some advice instead of just quoting the relevant regulation. I'll contact the inspection engineers and discuss with them.
 
Just received a couple of Electrical Danger Notifications (C2's) from our annual electrical inspections.

"No co-ordination between conductor and protective device cct 1T/P 2.5mm - 32A ref method B"

&

"High values of measured EFLI at ccts 6TP-15TP"

Could you offer some advice as to what these mean, as I'd like to have some understanding before I talk to our electrical contractor.

Thank you in advance.

Not quite sure in what context he is using coordination, there is no hyphen in the word. Not sure a 2.5mm cable and a 32 amp MCB can be classed as a "complex body but maybe as an activity"

Think it was an attempt of BS baffles brains
 
1- overload protectice device is too high for current carrying capacity of cable
2- efli is too high, you could reduce mcb size, upgrade cable size or install rcd 30mA on circuit which will give you max zs of 1667ohms.
 
1- overload protectice device is too high for current carrying capacity of cable
2- efli is too high, you could reduce mcb size, upgrade cable size or install rcd 30mA on circuit which will give you max zs of 1667ohms.

Thank you for you reply bigspark. With all the other replies, a little reading and having a good look at the circuits in question I've come to the same conclusion. Many thanks
 
If this is an ANNUAL report and the observations were not included in last years report there must be something remiss with any additions you have had done, or these observations have not been observed in the previous report.
If it is a breaker , or high efli on multiple circuits it is strange.

I must admit it is vague.
 
If this is an ANNUAL report and the observations were not included in last years report there must be something remiss with any additions you have had done, or these observations have not been observed in the previous report.
If it is a breaker , or high efli on multiple circuits it is strange.

I must admit it is vague.
The max Zs values are now lower than they were in previous years with the new amendment...
 
Not quite sure in what context he is using coordination, there is no hyphen in the word. Not sure a 2.5mm cable and a 32 amp MCB can be classed as a "complex body but maybe as an activity"

Think it was an attempt of BS baffles brains
It's how it's listed in the schedule of inspection now though isn't it.

Coordination of over current protective devices and cable size...or something along them lines...
 
If an RCD is already present in the system then it could be effecting the Zs readings. Had this multiple times and bypassing it or using the alternative Zs method proved it to be the RCD.

Obviously this depends on the current set up and if it is RCD protected or not.

One other thing regarding Zs values, If carrying out an EICR on an installation that was installed to say the 17th before any AMD's then if the circuits tested met these values then surely it complies to the edition/AMD it was installed to?
 
Last edited:
It's how it's listed in the schedule of inspection now though isn't it.

Coordination of over current protective devices and cable size...or something along them lines...

Yes you are spot on ...............coordination between conductors and overload PD's so hats off to the inspector on that one....and you Bright
 

Reply to A little help please. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
403
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
991
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
"A catalogue of errors" would be the appropriate phrase here and I agree with Avo and James that HSE need to be involved rather than this forum...
Replies
4
Views
2K
  • Article
EMailed to the forum for you @PCBWay
    • Winner
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top