When testing Ze on a TT the only connection between the line and the earth rod is the actual ground.

When you do a Ze is it actually sending a small current through the actual ground from the earth rod at the house to the earth rod at the transformer?

Also, related to the above, I have 2 separate garden light circuits. The customer complained of RCD tripping. The garden lights have junction boxes buried in the ground that lead on to the next light. These Jb's are full of water hence the tripping (IR results 0.006Mohms N-E).

With regards the above paragraph I am getting 0.15Mohms between the Neutrals of both separate garden light circuits (also the earths and line's but you would expect that as light bulbs are in and 0.006Mohms N-E). This is with all the conductors completely isolated, is this again because the separate circuits have a link via the actual ground (due to all the water in the buried JB's)?
 
When you do a Ze is it actually sending a small current through the actual ground from the earth rod at the house to the earth rod at the transformer?

Yes, although as Des says, there can be multiple paths from the mass of earth back into the distribution system cable as well as the substation earth, via bonded services on TN installations, both TN-S and TN-C-S.

an insulating material is a poor conductor but still a conductor,

Although theoretically true, resistivity is a property that has a wider variation than almost anything in human experience. The conductivity of Teflon is 100000000000000000000000000000000 times lower than that of copper, so it is a little misleading to call it 'still a conductor', when we can use materials 10000000000 times more conductive as insulators. Soil is much closer to copper than to teflon, so that does qualify as reasonably conductive given the rather large cross sectional area available.
 

Reply to A question about how current travels through the real earth? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
  • Question
Thanks for that guys I was more thinking about difference in potential between the tub and wet paving flags . The tub is plastic . But it’s the...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top