Hello all, long time no speak
I was talking to a mate of mine the other day about this place and he emailed me a question he set to a class of apprentices. I've not had a go at it (yet). Have a try-
3 single phase heating elements are fed from a 3 phase 4 wire 400 volt supply. Assume each element is 2KW at 230 V. The switch is in the neutral (once upon a time it was allowed)
Calculate the heat output
A with the switch open.
B with the switch closed
I have the answers but as I said above, I've not worked through it myself yet
 
Very good question indeed and I can see what reply your after which I'll leave to the Trainee's of course :)


TBH I would be interested to see this question in the main forum too after its run its course in here ... its a thinker for most levels
:devilish:
 
Last edited by a moderator:
Is it within your mod powers to copy and paste it into open forum or shall I just reproduce it when the time comes mate?
 
Is it within your mod powers to copy and paste it into open forum or shall I just reproduce it when the time comes mate?

I know but was going to let it run as your little baby in here first ..didn't want to steel any thunder plus didn't want the Trainee's seeing the answer in the main forum which is the main reason to do it later ;)
 
could somebody explain to me how to work it out please?

With trev's agreement I'll ask Marvo to undelete his post which is a wiring layout to better explain what is happening, now that the answer is out there I don't think there is any issue to explaining indepth the reasoning behind the answer.
 

Reply to A question from a mate in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
441
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

As long as the heat input is greater than the heat losses from the container and the resistance is sufficient to limit the current to no more than...
Replies
2
Views
219
davesparks
D
The total current capacity of the system in amperes is the same as the per-phase rating when referring to a balanced three-phase system. Thus, a...
Replies
4
Views
674

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top