an a.c load has an output power of 12 kw and an input of 15 kva. determine the reactive power

can anyone work this out it looks simple but i cant remember what to do again
 
KVAr^2 = KVA^2 - KW^2

Or use KVAr = sqare root of KVA^2 - KW^2

KVAr = sqare root of 225 - 144

= 9 KVAr
 
Heres a weird one

what are the copper losses in the primary winding of a step up tansformer, where the resistance of the winding is 0.3 ohm and the transformer is drawing 8 amps from the supply ?

any Ideas IQ ?
 
ive got more

what is the current that can be drawn from a 100va transformer if it has an out put voltage of 20 v


another is

if a transformer has a maximum output voltage of 200v and supplies a current of 12a what is the KVA rateing of the transformer
 
P=VI

KVA translates into Kilo volt amperes
KVA is apparent power, and Kw is real power.

So to work out apparent power, you multiply the real power by thepower factor. As you haven't given me a power factor, i asuume unity ( a power factor of 1).

So in other words, KW and KVA are one and the same, with a power factor of one.
 
some more if thats ok and youve got time

a single phase transformer with 2000 primary turns and 700 secondary turns is fed from a 230v ac supply determine the secondary voltage


a transformer haveing a turns ratio of 2.8 (primary to secondary) is connected to a 230 v supply. calculate the output voltage
 
some more if thats ok and youve got time

a single phase transformer with 2000 primary turns and 700 secondary turns is fed from a 230v ac supply determine the secondary voltage

= 700/2000 x 230 = 0.85 v is that right

a transformer haveing a turns ratio of 2.8 (primary to secondary) is connected to a 230 v supply. calculate the output voltage

= = 8/2 x 230 = 920 v is this right

When a current of 200mA flows into a capacitor for 40mS, the charge developed in the capacitor would be ???

I dont suppose anyone knows the answer for this
 
Last edited by a moderator:

Reply to a strange question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
831

Similar threads

Hello Ric2013, MJPD29 and westward 10. I have a multimeter that I tested the voltage with and before I open the socket up I use a plug in tester...
Replies
4
Views
1K
  • Question
"So the question is to register with NICEIC/NAPIT for part P regs will they require other proof of qualification?" Why not contact them and ask...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top