My boiler is still working fine and my new Hive thermostat works manually (just not on the app).

The boiler regardless of what’s happening still shows the A21 fault which I believe is an RF signal fault? Any ideas?
 
A21 will almost certainly relate to a built-in Worcester bosch wireless thermostat and not the Hive unit.

I suspect the boiler had a Worcester bosch thermostat originally which has now been replaced by a Hive thermostat. If the original thermostat receiver wasn't fully removed from the boiler it will still be looking for that thermostat connection and throwing up the error as it is missing.
 
A21 will almost certainly relate to a built-in Worcester bosch wireless thermostat and not the Hive unit.

I suspect the boiler had a Worcester bosch thermostat originally which has now been replaced by a Hive thermostat. If the original thermostat receiver wasn't fully removed from the boiler it will still be looking for that thermostat connection and throwing up the error as it is missing.
Hi Dave. Yes I threw the Worcester thermostat, how would I ‘fully’ remove from boiler?
 
Hi Dave. Yes I threw the Worcester thermostat, how would I ‘fully’ remove from boiler?

That'll be why it's throwing up the fault code then!

You would need to remove the receiver from the boiler, depending on exactly which model of boiler you will likely need to re-fit the blanking plate in its place.

Obviously you should only do this if you are competent to open up the boiler and put it back together correctly.
 
That'll be why it's throwing up the fault code then!

You would need to remove the receiver from the boiler, depending on exactly which model of boiler you will likely need to re-fit the blanking plate in its place.

Obviously you should only do this if you are competent to open up the boiler and put it back together correctly.
It is a Worcester Comfort RF I believe. I’d be happy to do so, what will I need to disconnect?
 

Reply to A21 fault on Worcester boiler in the Central Heating Systems area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
356
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
909
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

U
  • Article
Smart thermostat causing boiler to short cycle or something else? Hi all, When I use my hive thermostat in the way I think your supposed to...
Replies
0
Views
142
u0362565
U
P
  • Article
Worcester Bosch Greenstar Regular Boiler - Always ON Morning all, I've noticed very recently that our Worcester Bosch Boiler is constantly ON and...
Replies
0
Views
265
Pgeddon
P

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top