Hi, could someone please tell me what cable size/type they would use on a 3.6kwp pv system?Many thanks in advance
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Ac cable size ??? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
Id go for 4mm T&E if its domestic and you can back it up easily with 30 Ma RCD unit. Separate from existing RCD, I prefer. Or Go for 4mm2 SWA then it has the earthed sheath and is protected by nails screws and the like and doesnt need the 30mA RCD protection. Might be seen as over the top but to acheive the 1% volt you wont be far off I think.
Do your cable calcs properly for a 1%VD, or follow manufacturers instructions. For all we know you have a 50m run.
you need to put it on its own RCD not on a RCD side of a 16th or 17th Edition board, ideally a high integrity board would be best with its own RCBO.