becuase a RCD has a disconnection time of 0.4 sec where the inverter has a disconnection time of 5 sec, so if the rcd trips the inverter will pump power down any circuits on that RCD side and you dont want that.
 
You are making up your own rules there which are not in 7671 or G83/1. Mostly disconnection times for inverters are below 5s.
Regards
Bruce
[ElectriciansForums.net] Ac cable size ???
 
Grandfortune a 30mA RCD which is the common one for domestic purposes is not 0.4 but 0.04 and as BruceB kindly posted most inverters disconnect well below your 5s disconnect time.

So why are the powers to be advising that a PV system needs to be on separate protection? I was told once on here that it is because of regulation 314.2, and I would dispute that also
 
With regards to Solar and Reg 314.2 kind of needs to be looked at in reverse. You dont want the PV system taking out the RCD protecting the remainder (or half of) the property circuits. I always provide a dedicated/protected circuit either by a single way CU on a henley, or a dedicated RCBO. More good practice than by the regs (litterialy)
 
Thanks Graeme but why are inverters taking out RCDs. I install many small stand alone UPS systems here all on RCD protection and very very few have taken out RCDs, even when they have had mains power failure.

This is what I'm asking, is it because of the start up every morning? Are there high protective conductor currents in use on the inverters that are used in PV installations?

Becasue if it is a case of protective conductor currents then should not reg 531.2.4 be cited?
 
@Malcolm, If I remember right the UPS's don't back feed do they? The current still flows the same way?
 

Reply to Ac cable size ??? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
270
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
771

Similar threads

R
  • Article
Radiator size Hi. Currently have 3 small double radiators (500x600) in our open plan living room/kitchen diner. Would like to change them for...
Replies
0
Views
93
robcharlton
R
Use wago connectors instead, much easier and safer I think
Replies
4
Views
496

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top