Hi All

This might be a dumb question but it occurred to me after having done my training that my understanding of the AC isolator location is not quite correct if the PV system was placed (say) on a garage roof.

So, from the inverter, I have an AC isolator to the garage consumer unit from the inverter. The inverter will be placed next to the garage consumer unit.

My question is, do I need a second isolator at the main house consumer unit which feeds the cable to the garage cu?

I can understand that if an inverter were placed in an attic (for instance) then a second is needed at the main consumer unit (as training course states) but in the 'double' consumer unit scenario, switching off the supply at the main unit still gives rise to a voltage supply from the garage cu/pv system.

Thanks for your help and as this is my first post, sorry if a dumb question.

Mike
 
Hi Mike, a single isolator in the garage is all that is required. Make sure you put a 'dual supply' sticker next to the CU in the house.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
AC Isolator at Garage C/U Question
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
1

Advert

Thread statistics

Created
MikeXl426,
Last reply from
gr7,
Replies
1
Views
2,218

Advert

Back
Top