Is it acceptable to use a spare core in a 4 core armoured cable to carry 12volts DC when other cores in the same cable are carrying AC mains?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss AC mains and low voltage DC in same cable? in the UK Electrical Forum area at ElectriciansForums.net
Is the ELV Ethernet insulation rated the same as 230 v cables?Is it permissible to run ELV Ethernet over LV 230V ac cables?
yep agreed I've re read it over and it does say system , I even wrote the dam thing on the thread.As I interpret it that is for the same wiring system, they have made a specific regulation exemption No' 6 for multicore cable as that does not fall under the term same wiring system due to the fact its a cable and not multiple cables or cores in a wiring system.
See further replies in the thread pal.This is interesting as I come across this a lot and never use the cable for ELV as worry about interference.......so you reckon there can't be an induced voltage due to the insulation Ian? Surely that can't be the case as you can get induced voltage from LV to LV? Or am I getting it wrong? Would be handy to be able to use the same cable for ELV and LV.
I would assume so, as the conductors used for the Ethernet are the ones already being used for the 230V.Is the ELV Ethernet insulation rated the same as 230 v cables?
Then no
I would assume so, as the conductors used for the Ethernet are the ones already being used for the 230V.
How will you get induced voltage on the dc circuit if the cores are insulated to the highest voltage present i.e. 230volts?
Just wondering why there has to be screening between cores in some multicore cables, when it's possible to use the same cores for both ac and dc?
As I interpret it that is for the same wiring system, they have made a specific regulation exemption No' 6 for multicore cable as that does not fall under the term same wiring system due to the fact its a cable and not multiple cables or cores in a wiring system.
It mentions wiring systems so if I read it again to me it's saying that if I have singles in conduit I can run band 1 and band 2 in the same conduit wiring system if each conductor is insulated to the highest voltage present i.e. 230 v.Hi - I'm going to stick my neck for purposes of a good discussion, and not saying I'd like to run 12V in the same multicore cable as 400V .
Reg 528.1, intro says no mixing Band 1 and Band 2 unless one of the 6 exemptions applies. Understood. I take it on board about the 6th method, but if we read it as a specific method for multicore cable, what about the 2nd method? Where it also says "each conductor of a multicore cable". Doesn't that mean there are 2 exemption methods for multicore cable? I haven't spotted why 6 should be read as separate from a wiring system but 2 should not
It's been a good discussion tho in which the forum is all about.Well in honesty I did say IMHO, yes I missed that part in point II @Wilko - and agree with both you and @Ian1981 on that.
I work on machinery to differing reg's and the reason for my take on this is safety under fault conditions, I see a big flaw in this regulation and I may raise it with the IET myself, but it would seem simply having the insulation value to the highest conductor would suffice, I would still consider the implications of the LV crossing over to the ELV and the potential risks associated with it if it were to occur, fusing alone isn't always a sufficient, like I said I said before, if DC is generated and isolated from the LV side in its generation then this could potentially create a accident waiting to happen.