Hi,

1% volt drop from the inverter to the consumer unit, is this 1% rule really required, or can i go above ?

Power one inverter ..

Thanks James
 
The Guide says it all really:

"The a.c. cable connecting the inverter(s) to the consumer unit should be sized to minimise voltage drop. A 1% drop or less is recommended. However in larger installations this may not be practicable or economic due to the very large size of cable resulting. In this case the designer should minimise voltage drop as far as possible and must remain within voltage drop limits as prescribed by BS 7671.
Note: The recommendation for a 1% voltage drop is due to two reasons: firstly when generating, the voltage at the inverter terminals is higher than the voltage at the supplier’s cutout – during periods of high power output this voltage drop must be kept to a minimum in order to prevent the inverter nuisance tripping on over voltage ; secondly the requirement ensures losses from the PV
system are minimised."

If you are the designer you have to make your mind up and then justify afterwards if required.
 
no excuse for not achieving 1% on a domestic install mind - at least not a standard one, maybe if you're doing ground mount a couple of hundred meters away down the garden or something.
 
I tend to design with 1% in mind. It does make it expensive on long cable runs but I would seriously hate to have to dig up and upgrade a buried cable if problems were experienced later.
 
yep, thanks again for your support i will work to the 1% rule
it's also important that you actually understand why this is important for solar PV rather than blindly following a rule.

In some situations even the 1% rule isn't really strict enough, and problems can result even if it's followed.
 
That's a fair point. Testing the incoming voltage is a pretty important part of a survey. But you do have to consider the possibility that grid voltages may rise.
 
Thanks again for the advice. i will check the incoming voltage and apply the logic. I have my MCS inspection next week so i hope all is well, but im still concerned about earthing the array frame work, DTI tree it will be, thanks again to you both James
 

Reply to Ac vd in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
749
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
976

Similar threads

  • Question
Hi All, Looking for some advice into my build. What I've basically done is add additional RCD protection to my 100% off-grid 12V 3300W Inverter...
Replies
0
Views
183
Hi all. OK... Let me just try and clear a 1" square space on the screen inbetween all the highly intrusive ads.... On a site (NHS in fact) and...
Replies
0
Views
487

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top