Doing my ACA on Monday.
Heard we should now be using rubber shielding and insulated crocodile clamps when doing a Ze.
How do you remove the earth cable and access the connections with this in place?
Can someone inform the procedure for this?

Cheers
 
remove earth cable from MET, AFTER ISOLATING THE INSTALLATION, then clip you croc on the earth cable.
 
No the croc clips are to hold the rubber sheet in place. I know how to carry out the test. It's the Health & safety sequence I need to know in regards to this rubber sheet.
thanks
 
I can't fit the life of me think why you would need a rubber sheet to cover any exposed conductive parts?
the tester will not allow a voltage of greater than 50v anyway, and you will have already verified that these parts are in fact bonded (where required) before the live tests take place.
also, can you imagine the amount of rubber that would be required in say a factory?

i really don't see the point!
 
nb the questions at the end are the hardest part if you are finding them tricky work from the back of the question paper to the front and take a bottle of water with you it gets quite warm when some random guy is asking you a million questions while youre trying to test something
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Aca
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
19
Unsolved
--

Thread Tags

Advert

Thread statistics

Created
thomas-1981,
Last reply from
Des 56,
Replies
19
Views
1,747

Advert

Back
Top