You never know with some of these forums, I've just been lambasted for dragging up an old post oooppppssss!!!
 
I used to work for a machine builders up until about 18 months ago and the box sections are always used for routing cables.
3 things to note,

1)the machines were designed with rectangular cut-outs at regular intervals on the machine to facilitate wiring/maintenance
2)entry into the box section was made by drilling and tapping 32mm (or 50mm if box was big enoough) and then a short reach bush screwed in with threadlock
3)a seperate box was used for power and comms/analogue cable run to avoid interference.

The company has been making machines for 30+ years and to my knowledge, nothing has ever come back because of running in the box sections. at the end of the day, it is hardly any different to running in trunking or steel conduit

Hope this helps

Virtually every machine build i've seen of any size, has been built to use the fabric of the machine for it's wiring and air piping systems etc. A good many also use them for flush mounted switches and push button locations... Basic standard practice i would have thought. Only ever seen singles run in box sections etc in very old machines, and i guess many of them are still around today giving sterling service. They don't make em like they used too, those old machines were built to last and last they did!! lol!!! Think they call it ''Over Engineering'' today...lol!!!
 
actually i recommend trunking the cables in raceway or conduit.
(had to completely rewire a carton erector after someone welded safety rails on a frame section carrying cabling)
lots more smoke than they expected and stink quite a bit.:lol:
they were un-aware that cabling was run in the framework
 
actually i recommend trunking the cables in raceway or conduit.
(had to completely rewire a carton erector after someone welded safety rails on a frame section carrying cabling)
lots more smoke than they expected and stink quite a bit.:lol:
they were un-aware that cabling was run in the framework

That's fine if there is enough space/room on the machine to incorporate a conduit or trunking system. Most manufactures will use the framework to route cabling, air, hydraulics etc, around the machine. Generally you wouldn't use the fabric of the machine to house the incoming supply cable, though i've seen that done a few times too....
 

Reply to Acceptable wiring methods for machine tool in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Article
I've sticked the post for you!
    • Like
Replies
2
Views
1K
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top