OK - this is a dual board, about 3 years old ......... 1 RCD per bank.

They are experiencing random tripping, and my trusty earth leakage clamp shows that both banks are running at around 21 mA leakage - so the smallest change plunges half the house into darkness etc.

Anyone know if I could easily source the parts to add 2 more RCD's (yes I realise some circuit consolidation would be required ....

Hager dual CU.jpg


Thanks

And no I didn't install this!
 
The cheapest place i have found recently for hager rcbos is
discount-electrical.co.uk also known as shop4electrical.
The price can vary widely between suppliers. Hager are good with 2 year warranty too in event of failures. Dodgy batc etc...just never buy direct from hager though. They charge the list price!
 
Even if you manage to split that lot over an extra couple of RCD's there's no assurance that nuisance tripping of a bank of circuits will not be a regular occurrence. The client will likely assume that whatever you do will be a total cure.
I'd insist on fitting RCBO's regardless of cost.
 
I had the same issue on a stackable Hager 36 way board. Lots of electronics and control system were leaking due to design.

We added another neutral bar and put rings, cooker and kitchen on rcbo's. Problem went away, I think adding an RCD would be more hassle than it's worth.
 
How does adding another neutral bar solve the problem ?
The only thing that makes sense is that it lowers the neutral systems impedance.
In which case that indicates a failing or poor neutral system to start with.
 
How does adding another neutral bar solve the problem ?
The only thing that makes sense is that it lowers the neutral systems impedance.
In which case that indicates a failing or poor neutral system to start with.

Adding a neutral bar would enable RCBO's to be added .... then the higher leaking circuits could be on them, reducing the cumulative leakage on the current RCD's.

Having 13 MCB's on RCD wasn't a great idea to start with!
 
How does adding another neutral bar solve the problem ?
The only thing that makes sense is that it lowers the neutral systems impedance.
In which case that indicates a failing or poor neutral system to start with.

Too much earth leakage going through the rcds . adding another neutral bar allows the earth leakage to be split across more devices .
 
Adding a neutral bar would enable RCBO's to be added .... then the higher leaking circuits could be on them, reducing the cumulative leakage on the current RCD's.

Having 13 MCB's on RCD wasn't a great idea to start with!
Never seen a 13Amp cb
 
it's OK pete. i'm feeling the early stages of dementia also, just forgot where i'd put my beer down. :D:D
 
never mind, pete, aldi is open till 21.00 hrs. send mrs. pete out. if you're lucky, might get a pie as well.
 
never mind, pete, aldi is open till 21.00 hrs. send mrs. pete out. if you're lucky, might get a pie as well.
Not possible for Mrs Pete999 to get about much these days Tel, and to be honest I really can't be bothered, as well as the drink driving issue, I'LL wait till I get back from ELEX tomorrow. Pick up 1 or 6 on the way home.
 
i'd go elex if it wasn't so far. it's only the munchester that's viable for me.
 
you just can't get through to a woman. it's like...

she: why have you spent £60 on them super rods?

me: because i need them.

she: how on earth did you manage to cable them new downlights in my kitchen?

me: super rods.

Tel 1 - mrs Tel 0.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Adapt this CU...........
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
38
Unsolved
--

Thread Tags

Advert

Thread statistics

Created
Octopus,
Last reply from
weevilward,
Replies
38
Views
3,180

Advert

Back
Top