Adding a consumer unit. | Page 2 | on ElectriciansForums

Discuss Adding a consumer unit. in the UK Electrical Forum area at ElectriciansForums.net

Ginner

-
Joined
Jul 30, 2016
Messages
14
Reaction score
6
Location
East Yorks
Good afternoon and please go easy with me as. I have recently completed my time with one of the services and now wish to become an electrician. My studies are going well but from time to time I lose my way. The question I'd like to ask based on:
  1. The property in question has a 100amp supply
  2. The original consumer unit is working to more or less full supply/capacity
  3. The customer would like an additional CU to supply a workshop which contains a 5 potters wheels ([email protected])
My thinking is because you are drawing near capacity of the 100amp supply, allowing for diversity, this request would not be a feasible!
Look forward to your valuable comments.
 
Thanks for your advice really appreciate your input :)

Hi Ginner - If you are on an active training course, it might be in your interest to apply for access to our training forum, its and area more suited to ask the types of questions that someone learning the ropes may ask and has selected members who will help answer your queries in anyway they can. Its not essential to be in the Trainee Forum and is only a recommendation.
 
Or you're growing certain plants? (for medicinal use :) )

Lol no cant stand the smell. No what I thought was a simple question has turned out to be not. I'm looking at it from the angle, if a property was close to the 100amp capacity (please check out my diversity calcs earlier) and required additional supply, how could a second consumer unit be added,that's if it could?
 
The problem with the "diversity" calculations is that they were thought up when fuseboards had 4 or maximum 6 MCB's - so the calculations "worked" but these days properties often have 10 or more MCB's or RCBO's but the demand is often less.....

I would add up the breakers and multiply by 0.25 and see what you get!

PS what's happened to the "like" button?
 
The problem with the "diversity" calculations is that they were thought up when fuseboards had 4 or maximum 6 MCB's - so the calculations "worked" but these days properties often have 10 or more MCB's or RCBO's but the demand is often less.....



I would add up the breakers and multiply by 0.25 and see what you get!

PS what's happened to the "like" button?

Great thanks for info, this is what I keep coming up against, old stuff used in this modern age ie lighting based upon 100w fitting for calculation purposes!

PS if I could find the like button I would use it, sorry I'm new to this and it's operation. I have found a thumbs up icon for your message (i think) thanks again.
 
Lol no cant stand the smell. No what I thought was a simple question has turned out to be not. I'm looking at it from the angle, if a property was close to the 100amp capacity (please check out my diversity calcs earlier) and required additional supply, how could a second consumer unit be added,that's if it could?

No standard domestic dwelling property will ever come close to 100A for any significant sustained period. I have never seen a domestic main fuse blown due to overload yet. Faults yes, but not overload, and that's also considering that a huge proportion of properties have 60A fuses.

Diversity is half dark art, half guesswork, both of those halves based on experience. I would not worry too much about it for now and concentrate on the OSG method of working diversity as that is, more often than not, what you will be asked to base answers on, however inaccurate it may be.
 
No standard domestic dwelling property will ever come close to 100A for any significant sustained period. I have never seen a domestic main fuse blown due to overload yet. Faults yes, but not overload, and that's also considering that a huge proportion of properties have 60A fuses.

Diversity is half dark art, half guesswork, both of those halves based on experience. I would not worry too much about it for now and concentrate on the OSG method of working diversity as that is, more often than not, what you will be asked to base answers on, however inaccurate it may be.

Agreed.
One substantial house we look after has 5 beds,2 shower rooms,a huge kitchen with every appliance you can think of as well as an electric aga,9kw of floor heating and a 12kw hob.....all been running on a 60a fuse for years.
 
Lol no cant stand the smell. No what I thought was a simple question has turned out to be not. I'm looking at it from the angle, if a property was close to the 100amp capacity (please check out my diversity calcs earlier) and required additional supply, how could a second consumer unit be added,that's if it could?

Ah, if the installation is actually at maximum capacity, or the proposed additions will take it over that capacity then the solution is to arrange for a larger capacity supply to be installed.

Single phase supplies over 100A are pretty rare and you would normally have to have a TP supply fitted (or possibly a second phase supplied at the DNO's discretion)
 
No your question is not to inflammatory at all, it's not a real job, it's a scenario I have thought up which I may come across in the future. I'm asking the question because I would like to know the answer with the help of you experienced sparks. My diversity workings are as follows based on counting the circuits and relying purely on design:

Typical dwelling 100amp supply.
Lighting (Diversity 66% of total current demand)

Ground floor 7 lamps @100w = 700w (700x66=396w/230 = 3amps) 3amps

First floor 6 lamps @ 100w=600w (600x66=396w/230 = 1.72amps) 2amps

Ring finals

Kitchen 100% of current demand 32amps

Ground floor Diversity 40% of current demand=12.8amps 13amps

First floor Diversity 40% of current demand=12.8amps 13amps

Other items

Cooker & Hob 11.5Kw (11.5/230=50amps) (first 10+30%remainder no socket) 22amps

Immersion 3Kw (3000/230=13amps) no diversity allowed 13amps

Total 98amps

Ps: With a Shower
Shower 8.5Kw (8000/230=37.8amps) no diversity allowed 38amps


New Total with a shower 135amps

As a trainee I would appreciate constructive help please.

I only finished college last year and I was taught to just do it this way in a real world scenario and also was told to do it this way in my final exam for working out max demand for the EIC, just add up all the mcb/rcbo and x by o.4 and use that as max demand.

Presuming up and down lighting are on separate circuits and up and down sockets are also separate.
Up lighting = 6amp mcb
Down lighting = 6amp mcb
Kitchen sockets = 32amp mcb
Down sockets = 32amp mcb
Up sockets = 32amp mcb
Cooker/Hob = 50amp mcb (just going by size)
Immersion = 16amp mcb

Total = 174Amps

174/0.4 = 69.6 rounded up to 70Amp (and even that I would say is quite a bit higher then actual reading)

Add in the shower 40amp mcb takes it to 214Amps.

214/0.4 = 85.6Amp total

So I would say add whats needed no problem.
 
Last edited:
I only finished college last year and I was taught to just do it this way in a real world scenario and also was told to do it this way in my final exam for working out max demand for the EIC, just add up all the mcb/rcbo and x by o.4 and use that as max demand.

Presuming up and down lighting are on separate circuits and up and down sockets are also separate.
Up lighting = 6amp mcb
Down lighting = 6amp mcb
Kitchen sockets = 32amp mcb
Down sockets = 32amp mcb
Up sockets = 32amp mcb
Cooker/Hob = 50amp mcb (just going by size)
Immersion = 16amp mcb

Total = 174Amps

174/0.4 = 69.6 rounded up to 70Amp (and even that I would say is quite a bit higher then actual reading)

Add in the shower 40amp mcb takes it to 214Amps.

214/0.4 = 85.6Amp total

So I would say add whats needed no problem.

This is the sort of thing that helps
 

Reply to Adding a consumer unit. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
395
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
980
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
787
  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top