A definition of a cpc also says connecting exposed conductive parts of equipment to the MET of which there would be no exposed parts of class 2 equipment.The definition of a cpc is a conductor that is connected to the MET.
So I would read 411.3.1.1 as each point requires a conductor that is connected to earth.
612.2.1 requires that continuity of protective conductors is carried out during testing.
132.16 requires that all existing equipment and arrangements are suitable for safe alteration before the work is carried out.
I would personally not extend a circuit with no cpc.
It mightn't be more dangerous, but it would still fail to meet the minimum safety standard for electrical installation work, i.e. BS7671.the wiring will be no more dangerous than previous with a relivant note on a MWC
You could of course connect a cpc to that of another circuit. However if it is not mechanically protected then the minimum cross-sectional area of this cpc will be 4mm^2.I would personally not extend a circuit with no cpc.
Why? It's changing a pendant to 3 down lights.It mightn't be more dangerous, but it would still fail to meet the minimum safety standard for electrical installation work, i.e. BS7671.
Why would it fail to meet BS7671? Quite simply because it wouldn't comply with it.Why? It's changing a pendant to 3 down lights.
By that logic a lighting circuit containing no cpc must not be re-energised when renewing a consumer unit even with class 2 fittings fitted and suitably labelled which is allowed by bs 7671Why would it fail to meet BS7671? Quite simply because it wouldn't comply with it.
Firstly replacing a distribution board is quite different as you are not altering the existing circuit (leaving aside the protective device for now). So you are only required to verify your installation work (namely the replacement distribution board) - so you would ensure that the protective devices will operate in the time required. It doesn't mean that you are taking responsibility for installation methods; core colours etc.By that logic a lighting circuit containing no cpc must not be re-energised when renewing a consumer unit even with class 2 fittings fitted and suitably labelled which is allowed by bs 7671
Firstly replacing a distribution board is quite different as you are not altering the existing circuit (leaving aside the protective device for now). So you are only required to verify your installation work (namely the replacement distribution board) - so you would ensure that the protective devices will operate in the time required. It doesn't mean that you are taking responsibility for installation methods; core colours etc.
Secondly, you state "with Class II fittings fitted and suitably labelled which is allowed bs BS7671". Can you quote where BS7671 suggests that this is acceptable, or prescribes any label for this eventuality? I can assure you that it is not contained within BS7671.
Well I'd say if it's selv then the cpc is required to be not connected to the primary side of the sourceWhilst researching this topic, I found reg 412.2.3.2, which I'll let you chaps read and explain, cos my heads hurting now.
On this point, would running a cable from a 12v dc transformer, to a remote luminaire require a cpc?
Reply to Adding a light to a circuit with no earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net