uksparks
-
Hi,
What are your thoughts on adding a further 63A load to this board? It will be using 63A too, not just a few amps of it as its a for a twin car charger.
looking at it, theres a max load of the following if everything was maxed out.
L1: 126A
L2: 193A
L3: 211A
I need a 63A single phase supply, so my gut instinct says put it on L1, but to you feel im adding a lot of extra load to the board? I know its not a huge amount but just wondering what your thoughts were?
Obviously taking diversity into account etc, its not over the top, its only an office. The two 63A supplies on L2 and L3 on 35 and 36 are not in use at the moment but will be shortly.
The other part of the issue is, getting armoured cable out of the wall, its got to come from about 2.5 meters up the wall, down then into the ground. I don't really know which way to tackle this as I want it to look really neat and tidy for the customer. The cable is then going into the ground outside.
I can get away with 10mm SWA to feed the charger unit, but not 100% sure the best option really to get it looking nice on the wall, then theres this bit at the bottom at juts out.
I did look at running non armoured cables to an adaptable box on the outside then glanding the SWA to that and straight down, but ideally i don't want to use an RCD / RCBO to feed it as the unit has two RCBO's built into it.
What are your thoughts on adding a further 63A load to this board? It will be using 63A too, not just a few amps of it as its a for a twin car charger.
looking at it, theres a max load of the following if everything was maxed out.
L1: 126A
L2: 193A
L3: 211A
I need a 63A single phase supply, so my gut instinct says put it on L1, but to you feel im adding a lot of extra load to the board? I know its not a huge amount but just wondering what your thoughts were?
Obviously taking diversity into account etc, its not over the top, its only an office. The two 63A supplies on L2 and L3 on 35 and 36 are not in use at the moment but will be shortly.
The other part of the issue is, getting armoured cable out of the wall, its got to come from about 2.5 meters up the wall, down then into the ground. I don't really know which way to tackle this as I want it to look really neat and tidy for the customer. The cable is then going into the ground outside.
I can get away with 10mm SWA to feed the charger unit, but not 100% sure the best option really to get it looking nice on the wall, then theres this bit at the bottom at juts out.
I did look at running non armoured cables to an adaptable box on the outside then glanding the SWA to that and straight down, but ideally i don't want to use an RCD / RCBO to feed it as the unit has two RCBO's built into it.