Hi,

What are your thoughts on adding a further 63A load to this board? It will be using 63A too, not just a few amps of it as its a for a twin car charger.


[ElectriciansForums.net] Adding an furth 63A load[ElectriciansForums.net] Adding an furth 63A load

looking at it, theres a max load of the following if everything was maxed out.

L1: 126A
L2: 193A
L3: 211A

I need a 63A single phase supply, so my gut instinct says put it on L1, but to you feel im adding a lot of extra load to the board? I know its not a huge amount but just wondering what your thoughts were?

Obviously taking diversity into account etc, its not over the top, its only an office. The two 63A supplies on L2 and L3 on 35 and 36 are not in use at the moment but will be shortly.

[ElectriciansForums.net] Adding an furth 63A load

The other part of the issue is, getting armoured cable out of the wall, its got to come from about 2.5 meters up the wall, down then into the ground. I don't really know which way to tackle this as I want it to look really neat and tidy for the customer. The cable is then going into the ground outside.

[ElectriciansForums.net] Adding an furth 63A load[ElectriciansForums.net] Adding an furth 63A load

I can get away with 10mm SWA to feed the charger unit, but not 100% sure the best option really to get it looking nice on the wall, then theres this bit at the bottom at juts out.

I did look at running non armoured cables to an adaptable box on the outside then glanding the SWA to that and straight down, but ideally i don't want to use an RCD / RCBO to feed it as the unit has two RCBO's built into it.
 
It's hard to tell without measuring etc but from what I see L1 is the least loaded phase, if the last 2 ccts are only small offices then can't you fuse them down to 32amp then that way it'll go a long way to stop them being abused in the future by numpty sparks who'll see them as 63 amp available load.
Edit:
What are the numbers referring to written in biro on the left hand side, are they the actual circuit numbers?
 
To be honest I have no idea, thats all written on a piece of plasterboard propped above the distribution board... not very good for a new install is it, i dread to think what it will look like inside.

Yes thats not a bad idea, I could drop them down to certainly 40A breakers which would assist, or like you say 32A, that then frees up a bit, to be honest, i bet they are only pulling less than 10A anyway, ill have to measure it.

What do you think about the outside bit? I don't know what to suggest.
 
If the cable is being buried then SWA externally certainly, to get it to ground level use galv trunking as that wont look out of place attatched to the outside of that type of building.
 
having spare capacity in the DB is only half the story , you need to check the potential of whats upstream.

and i'd use 50mm tray on top hat brackets for the cable run down the side of the building then cleat along that row of bricks above the gravel , with strip grommet and silicon for the wall penetration.
 

Reply to Adding an furth 63A load in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I answered a similar question for the client, just looked at all the heaters (2KW per heater) and then asked for their half hour consumption...
Replies
7
Views
837
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
784

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top