Since when have SFCUs needed RCD protection?!?! If the cable is surface mounted then add an SFCU for each appliance and a flex outlet below.

Some people seem to think that you need to whack an RCD on anything with an electron! :D "Sorry sir, I can't change the socket for you because the RCD protecting it isn't RCD protected, and the regs need me to RCD protect the RCD protection protecting the RCD protection. Also sir, that wooden front door of yours, is that...."
 
Since when have SFCUs needed RCD protection?!?! If the cable is surface mounted then add an SFCU for each appliance and a flex outlet below.

Some people seem to think that you need to whack an RCD on anything with an electron! :D "Sorry sir, I can't change the socket for you because the RCD protecting it isn't RCD protected, and the regs need me to RCD protect the RCD protection protecting the RCD protection. Also sir, that wooden front door of yours, is that...."


The cables are not surface mounted they are to be buried but not over 50mm, also some of the sockets are being moved, so therefore they will all need protection by RCD as I understand it as they will all be on the same circuit and the newly moved sockets can be used for portable appliances.
 
The cables are not surface mounted they are to be buried but not over 50mm, also some of the sockets are being moved, so therefore they will all need protection by RCD as I understand it as they will all be on the same circuit and the newly moved sockets can be used for portable appliances.

You have six options available to you then:

1. Protect cables buried in walls in galv conduit or earthed galv capping and add RCD socket outlets/RCD SFCUs protecting socket outlets.
2. Use FP200, MICC or SWA in the walls and add RCD socket outles/RCD SFCUs protecting socket outlets.
3. Utilise electrical seperation as your protective measure so you don't need RCD protection.
4. Get the homeowner to become a fully qualified electrician so he becomes a qualified person thus the install not needing RCD protection.
5. Change CU to incorporate RCD protection.
6. Add a stand alone RCD in line with the kitchen ring/radial circuit.

I know which two of those six I'd be leaning towards :D
 
Can't use FP200, on it's own, would still need another acceptable method of additional protection.
The skilled or instructed person exemption does not apply to domestic premises, as there are no Statutory Requirements, which pertain to them.
pBit confused as to why the OP states they intend installing a plug in MCB.
 
I always thought FP had an earthed metallic sheath that would make it suitable for that purpose, not that I've ever used it for such purposes or even thought about it. With regards to the instructed person comment, it was clearly meant in jest, as was turning the customers kitchen in to an electrically separate installation :D
 
Must be rcd protected fused spurs to meet regs. Also the cable from the ring to the rcd spurs, needs to be mechanically protected or visibly surface clipped.
I've previously converted the existing socket into a dual box (single socket with the rcd spur. This overcomes the connection wire difficulty above.

Finally, it's work being done in a kitchen so it must be LABC notified and that means a test report - easy if you are registered as you probably know??

Whats a test report?
 
I always thought FP had an earthed metallic sheath that would make it suitable for that purpose, not that I've ever used it for such purposes or even thought about it. With regards to the instructed person comment, it was clearly meant in jest, as was turning the customers kitchen in to an electrically separate installation :D
It does have an earthed metallic sheath, unfortunately the cable is produced to a standard, not acceptable for it to be used in this situation.
The cables that would be acceptable, are manufactured to BS5467 (similar to FP200), or an SWA cable.
Yes I figured it was said in jest, but I figured, what the hell, I'm piping up about the FP, might as well remind people why we are not required to provide RCD protection in non-domestic installations.
 
A Question ? when a Socket is for an applience does it not also state somewhere that if its a labeled item and not used for anything else, it can be used without RCD protection, as the item is getting added to the rear of the applience can you not state the RCD is not required for this socket as its behind the unit, but also add that there is a recommendation for future upgrade to the Property.

Im new to this principle, but i have seen the option somewhere, not sure its application...
 
The requirement, is that sockets for use by ordinary persons and that are intended for general use, should be provided with RCD protection.
As such, a socket that is intended for a specific item of equipment (irrespective of who will be using it) does not require RCD protection.
There is an exception to the requirement for RCD protection, where a socket is intended for a specific item of equipment, and is labeled or otherwise identified as being for that purpose.
I don't understand why the wording of this Regulation hasn't been sorted out yet, the exception is clearly superfluous.
 
It does have an earthed metallic sheath, unfortunately the cable is produced to a standard, not acceptable for it to be used in this situation.
The cables that would be acceptable, are manufactured to BS5467 (similar to FP200), or an SWA cable.

I thought 5467 was SWA?

My understanding was that a cable buried in a wall had to be either suitably mechanically protected from penetration by screws, nails and the like or had to incorporate an earthed metallic sheath. SWA is never going to protect a cable from a screw or nail, it's armour is purely there (in the circumstance of being buried in a wall) to provide earthed protection to ensure ADS, as would the earthed metallic sheath of MICC, FP200 or suitably glanded SY?

Is it down to the csa of the armour/sheath? Obviously you can't use the FP's or SY's metallic sheath/braiding as a CPC unlike SWA or pyro. I'm guessing if it is unsuitable to be used as a cpc then it must be unsuitable to be used to protect the cable as a result of penetration damage?

Wish I had my BGB to hand as I love digging up little gems like this :D
 
Sorry wrong end of the list.
Its BS8436 cables that are similar to FP.
Trade names such as flexishield, and guardian, probably others.
The metallic sheath and the CPC have to sufficiently robust to withstand a specific fault current caused by piercing the cable with a nail or screw.
As far as I'm aware, the metallic sheath on FP type cables provides protection against heat, it is not sufficiently robust to carry the specified fault current.
 
Ah yes, I've used Flexishield before in a hospital. From what I remember it wasn't much different from FP look and feel wise. I'm guessing it all comes down to product spec and testing. I guess FP hasn't been through/passed the same tests as Flexishield in order to gain 8436.
 
As I recall, originally, flexishield was only suitable for low current applications, such as lighting, alarms and heating controls.
I understand they now have, and have had for some time, a product suitable for medium current applications such as socket-outlet circuits.
However, I'm not certain whether they have produced a suitable product for high current applications such as cookers or showers?

Yes it does look and feel remarkably similar to FP.
Probably can be used instead of FP?
 

Reply to Adding fused spurs for appliances to existing ring no 30ma RCD old fuse box ? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

There's a difference between being required to install an RCD and being required to have a full rewire when all the houses around have similar...
2
Replies
19
Views
1K
No to all. Also would require a means of isolation for PIV - pulling a fuse wouldn't be acceptable. I don't mean to seem disrespectful, but this...
Replies
1
Views
1K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top