Bender

-
Joined
Mar 18, 2019
Messages
21
Reaction score
2
Location
London
Adding a light to a Radial Power Circuit - the circuit is wired in 2.5mm and on a 20A MCB

Now if I add a FCU to my Radial and then wire my light in 1.5mm this should be safe?

But what if I don't use a FCU but wire the light with 2.5mm cable? what dangers are there.
 
Thank you for your Reply I'm a student and trying to better understand Overcurrent.

So im making notes, so apart from Isolating the light there is no danger in the second method as the MCB would safely protect the 2.5 cable from overload?
 
If your light is being controlled through a normal light switch, these are generally rated at 10A and can be difficult to terminate 2.5 mm into.

Switched fused connection unit with 5A fuse, using the switch to control the light is a good suggestion
 
Ok so the switch itself might not have the Load carrying capacity? and in theory could be dangerous with the conductors inside reaching a dangerous level of heat before the 20A MCB tripped?
 
I guess what im driving at is as I understand the MCB is protecting the cable from Overload but Lighting circuits usually run of a lower rating MCB so apart from the wires is anything else being protected from a lower rated MCB that im missing?

This is all hypothetical and just trying to understand overcurrent, MCB rattings and Cable CSA size :)
 
Theoretically possible to overload the light fittings if you're planning on running multiple lights.

The main issues with doing unconventional installations is that it can cause confusion for the 'next guy'.
 
In most domestic situations, I wouldn't want to be connecting 2.5mm cable into a light fitting terminals, either, they aren't designed for it.
edit. Just seen #4, sorry LS.
It's not just about protection, there's the basic common sense factor
 
Last edited:
Hi All - see Reg 559.5.1.204 which limits some lampholders to 16A OLCP. I was expecting to see 6A for pendants somewhere thereabouts, but can't.
 
In most domestic situations, I wouldn't want to be connecting 2.5mm cable into a light fitting terminals, either, they aren't designed for it.

Neither would I. But it is not uncommon to find a builder has wired up downlights in 2.5mm T&E. With all the exposed basic insulation hanging out of the fittings, of course!
 
Further trying to understand Overcurrent - In europe you have a Radial power circuit protected by a 20A MCB but all sockets are 13A and no fuse in plug so how is the cable of the 13A appliance protected from overload if the MCB is 20A?

Whats the current carrying capacity of flex for most appliances?

We have fuses protecting the flex from 32Amp on a ring but what about 20Amp on a radial?

So the original scenario could be dangerous with a pendant Light the flex not protected from overload by 20A MCB? so a fuse would be needed in this situation - unless pendant is of course wired in 2.5mm flex.
 
Last edited:
Don’t forget volt drop on power is 5% lighting is 3%

The 20a or 32a only protects the permanent installation from over current the fuse in a plug top would provide the protection for the cable
 
Further trying to understand Overcurrent - In europe you have a Radial power circuit protected by a 20A MCB but all sockets are 13A and no fuse in plug so how is the cable of the 13A appliance protected from overload if the MCB is 20A?

Whats the current carrying capacity of flex for most appliances?

We have fuses protecting the flex from 32Amp on a ring but what about 20Amp on a radial?

So the original scenario could be dangerous with a pendant Light the flex not protected from overload by 20A MCB? so a fuse would be needed in this situation - unless pendant is of course wired in 2.5mm flex.
Hi, just my late night thoughts :
- I expect the appliance should not be able to overload its own flex and maybe in Europe they have an internal fuse if it was required.
- appliances have flex with various current carrying capacity to suit their draw. Could be 0.5mm (3A) up to 1.5mm (16A) from Table 4F3A.
- in UK its expected that 13A outlets will use plugs with an internal fuse of 3A to 13A. The circuit overload protection rating is a separate issue.
- if wiring some lights off a circuit with power outlets I would always fuse it down as per the original advice from @telectrix :) . Looking in some lights their internal conductors don't fill me with confidence, just saying.
 
Last edited:
Thanks for your replys so this is what im going with yes it should be ok with the increase in CSA of the cable but because we don't know anything about the conductors in Switches and the Lights themselves and may have a rating below the CSA of our cable and could reach a dangerous level of heat before the MCB tripped from overload, a fuse would definitely be a good idea :)

The European and worldwide Radial and plugs not being fused I can only guess that a 0.5mm 3A rated flex on a 16A or 20A MCB is not realy ever been much of a concern although there does seem to be potential there for the conductor in the flex to fry before the MCB trips.
 
Last edited:

Reply to Adding Light to Power circuit. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
786
Haha yes, it is. Must be a northern expression. Have a Google 😂
Replies
3
Views
340

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top