So are you saying that this arrangement would not be acceptable?
T+E into a plastic JB which also has a 12volt tranny connected into it. I then run a 2 core cable to another plastic JB which has another tranny, and so on.
No Davey, not saying that atall - thats fine. The problem with the OPs proposed job was that it wasn`t a T&E supplying the TX - it was Twin & NoEarth - aka 2 core
Are the regs really insisting that we must run a cpc in, and connect it to nothing but itself?
In the case of SELV, certainly not. If you re-read post #15 you`ll see i`ve tried to clarify the distinction made between the various forms of `Protective Measures`. If the chosen method is SELV, a cpc can ONLY run to the end of Primary side - no connection to earth would be required nor permitted within the SELV cct itself.
My take on it is that, if you so desired, you could run a 2 core flex (of the correct size) from a light switch to a ceiling full of selv (as long as the tranny is double insulated as well) or double insulated light fittings. Whether thats a good idea or not is another question, but I cant see how its against regs.
Indeed ,you could argue that, provided that the switch was cpc`d then all beyond it (inc switch to tx cable) is not required to be connected to earth. But whilst i agree the Regs fail us on
this point, we would, of course, generously provide protection by ADS - by including a protective conductor within
that wiring system (e.g T & E)
Obviously, beyond point of connection to Double Insulated tx (Protective Measure in itself) the wiring system (2 core cable) would not require a cpc due to the Protective Measure of SELV.
But you couldn`t rely on Class II fittings alone as a Protective Measure, as you couldn`t ensure they don`t get swapped for Class I
Hope thats understandable enough...
Davey101;76379I said:
was about to say-
"I cant see how a cpc protecs a cable either, if you damage the insulation and the live core is exposed, having an earth inside the cable wont help you one bit.
True enough if you don`t simultaneously contact the cpc - ouch!
Davey101;76379I said:
If you cut right through the cable, then you have short circuit protection."
you sure do - thru the neutral or earth return paths.
Davey101;76379I said:
However, thinking about it, if you had a cable with no neutral, or earth,i.e a 3 core used for strappers, then cutting the cable would not result in ads.
Quite, thats why we use either earthed wiring enclosers or 3 core & earth.
& cheat with RCDs
But if your point relates to ...
Davey101;76379I said:
Is there a reg to say all cables must have a integral cpc?
...then obviously there couldnt be