Adding to circuits with no rcd (only mcb protection) | Page 2 | on ElectriciansForums
Discuss Adding to circuits with no rcd (only mcb protection) in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I'm guessing here, but I think the requirement for it to be surface mounted is to avoid any issues with damp in the fabric of the building.
Regarding people removing labels, anyone can remove any label at any time, that is their lookout. As long as you have complied with the regs, your job is done.
true but don't we have to consider the future of the installation,
would be a good thing to get outlets with imprinted wording like those for immersion heaters and cooker etc
guys just read page 22 on site guide, even with skilled people rcd required sockets up to 20 a
You may not have read the guidance correctly
Socket outlets in domestic installations and similar
A circuit supplying a specific labelled socket for eg, a freezer
As long as the cable is not buried,Rcd protection can be ommited
If it is buried then it has to have mechanical protection or be a protected cable
mate read again,
RCD MAY BE OMITTED FOR, SPECIFIC LABELLED SOCKETS SUCH AS A FREEZER,,, HOWEVER,,,,,,,BLA BLA BLA,,,,BUT ONLY CABLES ON THE SURFACE NOT IN A SPECIAL LO DONT NEED RCD
I think you are reading it incorrectly
quote
Cables installed on the surface do not require RCd
30 m/amp rcds are required for ii to vi above
A specific labelled socket blah blah such as a freezer
However the circuit must not require rcd as per v and vi above
That is buried without protection
If they are surface or buried with protection and labelled,no rcd
If they are surface and unprotected and labelled no rcd
If they are buried ,no mechanical protection,not permitted to label and rcd
As this is only an extra point for the boiler, as long as the extended circuit is >50mm in the wall, in metal/earthed protected sheath or surface run in trunking/conduit then no rcd/rcbo would be required, as a spur is feeding a item of "fixed equipment"
Reply to Adding to circuits with no rcd (only mcb protection) in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
No to all. Also would require a means of isolation for PIV - pulling a fuse wouldn't be acceptable. I don't mean to seem disrespectful, but this...
nicebutdim
N
Duh!!! Just re-read Op's original post, it was converted to a RFC!