D

Dru

I'm unsure as to what this regulation means.

Regulation 411.3.3

Can anyone put it in terms I can understand please? Not all sockets 20a or under require additional protection by the means of an RCD so what does it mean?

All help is greatly appreciated
 

Attachments

  • [ElectriciansForums.net] Additional protection regulation
    image.jpg
    385 KB · Views: 158
So a 16a radial with one socket requires an RCD?

Why does the rating of the OCPD have any relevance ? The regulation refers to the current rating of the socket outlet so don't apply it in other ways.
The socket most likely requires an RCD to protect it unless you are legitimately using a stated exception. Whether the circuit requires one is not clear from the information you have provided.
 
So as long as you haven't barried the cable the wall less than 50mm , and its not a domestic inviroment then i would way say part b of this reg covers what you have done as compliant
 
Surely exception b applies irrespective of the use of the building?
I did think that justvafter posting it i was under the impression that there was no exceptions for omitting an rcd in a domestic environment athough now i re read the reg it does not mention about it being a domestic environment so i stand corrected :)
 
Additional protection by a <=30mA RCD that trips in less than 40ms at 5 x rated current is NOT required for:

Socket(s) in a non domestic location that are designed to operate at <=20A where it has been identified through a written risk assessment that such additional protection is not required as there is not a significant risk.
A socket in any location that is designed to operate at <=20A where the socket is dedicated to a specific piece of equipment and the socket is labelled as such.
A FELV or a reduced low voltage system and mobile equipment for use in an outside location rated greater than 32A .


ALL other sockets that are designed to operate at <=20A DO require additional protection by a <=30mA RCD that trips in less than 40ms at 5 x rated current.
 

Reply to Additional protection regulation in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
has anybody tested the coffee machine for safety? I would try putting a normal load on the same supply as the monitor and see if that goes off at...
Replies
9
Views
755
Usually if there are only C3 observations it would usually be deemed satisfactory but could be found to be unsatisfactory in unusual...
Replies
15
Views
1K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top