I

iamelectric

doing a job at the moment , steel trunking from db to above a solid ceiling with klik lighting boxes mounted on the trunking , my question is do i need to install rcbos for the circuits as the flex coming from the light fittings to the klik boxes will just be lying above the ceiling with no mechanical protection?
 
10.7 Suspended ceilings
The conductive parts of a suspended ceiling will not introduce a potential that does not already exist in the space in which the ceiling is installed. In normal circumstances therefore, there is no need to arrange for the conductive parts of the ceiling to be equipotentially bonded, which would be unnecessary as well as difficult and costly to achieve.
The exposed-conductive-parts of Class I equipment are required to be connected to the MET of the installation by a protective conductor designed to conduct any earth fault current. Class II equipment is designed such that any basic insulation fault in the equipment cannot result in a fault current flowing into any conductive parts with which it may be in contact. The conductive parts of a suspended ceiling incorporating Class I and/or Class II equipment are not therefore intended to conduct an earth fault current, and so such parts need not be intentionally earthed. Some conductive parts of a suspended ceiling may be earthed, however, by virtue of fortuitous contact with the exposed-conductive-parts of Class I equipment.
The installation of all electrical equipment, including wiring systems above and incorporated in a suspended ceiling, should fully comply with the requirements of BS 7671 if the risk of electric shock from the ceiling is to be avoided. In particular, cables for fixed wiring should be supported continuously or at appropriate intervals, independently of the ceiling. The method of support is required to be such that no damage or undue strain occurs to the conductors, their insulation or terminations. Figure 10.8 shows a typical arrangement of supporting cables above a suspended ceiling
 
Heres how i see it dilb mate

The installation of all electrical equipment, including wiring systems above and incorporated in a suspended ceiling, should fully comply with the requirements of BS 7671 if the risk of electric shock from the ceiling is to be avoided

Then it says in particular cables for fixed wiring
 
10.7 Suspended ceilings
The conductive parts of a suspended ceiling will not introduce a potential that does not already exist in the space in which the ceiling is installed. In normal circumstances therefore, there is no need to arrange for the conductive parts of the ceiling to be equipotentially bonded, which would be unnecessary as well as difficult and costly to achieve.
The exposed-conductive-parts of Class I equipment are required to be connected to the MET of the installation by a protective conductor designed to conduct any earth fault current. Class II equipment is designed such that any basic insulation fault in the equipment cannot result in a fault current flowing into any conductive parts with which it may be in contact. The conductive parts of a suspended ceiling incorporating Class I and/or Class II equipment are not therefore intended to conduct an earth fault current, and so such parts need not be intentionally earthed. Some conductive parts of a suspended ceiling may be earthed, however, by virtue of fortuitous contact with the exposed-conductive-parts of Class I equipment.
The installation of all electrical equipment, including wiring systems above and incorporated in a suspended ceiling, should fully comply with the requirements of BS 7671 if the risk of electric shock from the ceiling is to be avoided. In particular, cables for fixed wiring should be supported continuously or at appropriate intervals, independently of the ceiling. The method of support is required to be such that no damage or undue strain occurs to the conductors, their insulation or terminations. Figure 10.8 shows a typical arrangement of supporting cables above a suspended ceiling

that's not a post, it's a bloody dissertation. :icon11:
 

Reply to additional protection? in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Fitted a lot of this sort of light recently, with all tests reporting back through central Dali controller(s).
2
Replies
15
Views
788
nicebutdim
N
  • Question
Thanks for the replies, I appreciate it.
Replies
4
Views
604

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top