Adiabatic equation Question | on ElectriciansForums

Discuss Adiabatic equation Question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

J

jimmer

I have just done a periodic on a flat that is supplied by 16.0mm pvc T&E (6.0 mm cpc only earth conductor) on a 60A 1361 switch fuse on a TN-S system. The DB Ze at the flat is 0.21 No matter what way i'm doing my sums i cant seem to get what i think is the right answer. I get 3.01mm minimum cpc is this right?
Any help much appreciated
 
Hi
With the info you gave I get 3.01 also.

But I thought that ZS should be used rather than ZE?
If you use the Max tabulated ZS for a 5sec disconnection (0.7 from table 41.4 p49), you get 230/.7=328.6 as I
I squared is then about 107958.
t from Fig 3.1 (p244) is then about 5sec on 328A
106958*5=539790 root=734.7
k=115
734.7/115=6.38

So assuming that your actual ZS is less than the 0.7 max, your 6mm CPC would be ok.

The 3.01 you had originally also just confirms that a 6mm would be ok - not that you should use 3mm.

But I really think it should be based on ZS

I hope this is helpful - and am more than happy to be corrected if I have gone wildly wrong on this:).

CH
 
Hi
With the info you gave I get 3.01 also.

But I thought that ZS should be used rather than ZE?
If you use the Max tabulated ZS for a 5sec disconnection (0.7 from table 41.4 p49), you get 230/.7=328.6 as I
I squared is then about 107958.
t from Fig 3.1 (p244) is then about 5sec on 328A
106958*5=539790 root=734.7
k=115
734.7/115=6.38

So assuming that your actual ZS is less than the 0.7 max, your 6mm CPC would be ok.

The 3.01 you had originally also just confirms that a 6mm would be ok - not that you should use 3mm.

But I really think it should be based on ZS

I hope this is helpful - and am more than happy to be corrected if I have gone wildly wrong on this:).

CH

The figure quoted was DB Ze (or Zs) at the board in the flat not at the main incomer, that was 0.07. It looks like the 6mm2 is ok as the cpc. Thanks to Des and Danny
 

Reply to Adiabatic equation Question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
I can't help wondering about earthing arrangements and how important aesthetics really are when attempting to make the best of a less than ideal...
2
Replies
21
Views
1K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top