Hi, If a storage heater has its own dedicated supply from an RCBO on the CU does it also need a fused spur? Thanks, Martin.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Fused spur for storage heater in the The Welcome Forum area at ElectriciansForums.net
As long as the rcbo is of the correct current rating then no.Hi, If a storage heater has its own dedicated supply from an RCBO on the CU does it also need a fused spur? Thanks, Martin.
Hi, if the storage heater has a duel supply then normally the convector side ie 24hrs supply should be fused to 13 amps as its normaly 2kw depending on size of heater .off peak side should be a 20 amp dp switch fed from 16 amp mcb /.rcbo fusing down the off peak side will eventually overheat the fuse /switch.same as 3 kw immersions
I agree but,Bad idea to run an immersion through a fused spur especially with the dire quality of accessories available today regardless of the manufacturer.
on a side note to that i remember connecting up a 3kw immersion a good few years ago when the manufactures stated a 13 amp switched fuse must be used .i didnt .you can hold your finger on the fuse holder and feel it heating lolBad idea to run an immersion through a fused spur especially with the dire quality of accessories available today regardless of the manufacturer.