Hi, If a storage heater has its own dedicated supply from an RCBO on the CU does it also need a fused spur? Thanks, Martin.
As long as the rcbo is of the correct current rating then no.
A 20amp isolation switch instead of the fused spur in that case.
 
Hi, if the storage heater has a duel supply then normally the convector side ie 24hrs supply should be fused to 13 amps as its normaly 2kw depending on size of heater .off peak side should be a 20 amp dp switch fed from 16 amp mcb /.rcbo fusing down the off peak side will eventually overheat the fuse /switch.same as 3 kw immersions
 
Bad idea to run an immersion through a fused spur especially with the dire quality of accessories available today regardless of the manufacturer.
 
Bad idea to run an immersion through a fused spur especially with the dire quality of accessories available today regardless of the manufacturer.
I agree but,
Its a real shame that we have to advise people that running any device at its rated current for long periods of time is likley to break it.

how do you think ford would get on if they recommended that you don't run there family car at 70Mph for long periods of time as it may overheat and fail prematurely!!
 
Bad idea to run an immersion through a fused spur especially with the dire quality of accessories available today regardless of the manufacturer.
on a side note to that i remember connecting up a 3kw immersion a good few years ago when the manufactures stated a 13 amp switched fuse must be used .i didnt .you can hold your finger on the fuse holder and feel it heating lol
 

Reply to Fused spur for storage heater in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
770
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
776

Similar threads

Replies
25
Views
1K
From the front cover of the manual: Newlec Helpline: 0800 783 6909 https://www.manualslib.com/manual/3408290/Newlec-Nlsh050.html#manual I think...
Replies
1
Views
190

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top