Can any one help please
on a tncs system (PME)
100amp main fuse bs1361 100amp
I am trying to work out the maths for the earthing is there a simple way all looks a little confusing
S is the csa of the conductor 25mm
I is ???
t is page 244 the table says 630A
K = ??
so 630A squared x 5 (5sec disconection time
Now I am stuck
Cheers
 
K is the value of the metal, whether it is copper or ally, from memory I cant remember what the values are, is root 3 used as well?, remember doing at college, but never applied it. Give me all the details you have, and I will run through Amtech for you.
 
If you know S = 25mm, then why are trying to work it out??
S is the figure you need to work out
I = current (squared), so its 100 squared x5
square root of
then divide by K
then that give S, (size of the earth)
 
If your looking to size the main earth and the cut out is the protective fuse:

I is the current required to disconnect, in t seconds
page 244 current to blow a 1361 100A fuse in 5 secs = 630A
t = 5 secs (as its over 32A)
K is from the tables on Page 129, if the earth cable is bunched with the tails then Table 54.3, 70degrees Thermoplastic and copper
K = 115

Therefore S= Sq Root(630 x 630 x 5)/115 = 12.25

So you need to use a 16mm earth!
 
S= size of conductor nominal conductor size mm2
I = fault current
t= time it takes, to operate device
K= thermal constraints of cable, temperature coefficient and heat capacity of cable.
 
Last edited by a moderator:
thanks yellowvanman
well confused now I have got that printed and in with the regs what I am trying to work out is the bonding sizes to water and gas
ie if I change a cu and I am trying to work out if I leave a 6mm cable is this ok??
Normal practise I upgrade to 10mm but customer has asked me to calculate because previous spark sais 6mm ok o/s/g has pictures of 10mm
sorry to confuse the matter what I am after is calculation for equopotential bonding many thanks
 
thanks yellowvanman
well confused now I have got that printed and in with the regs what I am trying to work out is the bonding sizes to water and gas
ie if I change a cu and I am trying to work out if I leave a 6mm cable is this ok??
Normal practise I upgrade to 10mm but customer has asked me to calculate because previous spark sais 6mm ok o/s/g has pictures of 10mm
sorry to confuse the matter what I am after is calculation for equopotential bonding many thanks

are you really a spark?................oh you must be your a member of the sparky arms

sorry could not resist :)
 

Reply to adiabatic equation reg 543.1.3 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
838

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top