If the supply is protected by a 100A fuse then the disconnection time required is 5 secs because its a distribution circuit and >32A. To get 5 secs disconnection the fuse needs to blow with 630A. If you get more - all well and good, fuse blows quicker.
Whilst Ze was 0.01 today what will it be in a few years when other houses are added to the road or other changes are made to the system - the only thing you can rely on is that the Ze will not be higher than 0.35 - because thats what the DNO has to provide!
Whilst Ze was 0.01 today what will it be in a few years when other houses are added to the road or other changes are made to the system - the only thing you can rely on is that the Ze will not be higher than 0.35 - because thats what the DNO has to provide!