you cant selecvt bonding conductors as 50% as a min telectrix????
Why can't you on a non TNC-S system ??
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss adiabatic on earth bonding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
you cant selecvt bonding conductors as 50% as a min telectrix????
Thanks Malcolm! Ok, so I should be using Ze. I think I sort of realised this when typing my post but thanks for confirming it.
Actually, I am feeling slightly embarrassed now - I was using the adiabatic to check final cct cable ratings last night so why I decided this morning to use the fuse trip current instead of the PEFC I don't know.
Ref 544.1.1. Again, I don't know why I missed that. I think the lesson is to not do sums with a hangover
Why can't you on a non TNC-S system ??
Shut up you lol ....................All this talk of Sunday Roasts, I have a chicken Swarma for my tea
As Tel said by using the 115 value your not going wrong as your erring on the side of caution, all your going to do is get a higher CSA value which in anything under 16mm is not going to be that expensive. Once your starting to go over that and it's running 60-70 metres then it can become an expensive mistake
In your scenario I would not consider a single earth conductor taped to a single SWA as "bunched". if there were 6/7 SWA and 6/7 Earth conductors all taped together and run together, then to me that would be "bunched", and I would use start to use table 54.3 and the lower value for safety.
In a way, you do use the fuse trip current.
If you had a PEFC of 500A, with a BS1361 fuse, you would either have to use the values in the table (460A and 5s), or determine from the graph at what the actual disconnection time would be (about 1.5s).
Where people often go wrong, is they use the time value from the table, along with the measured value of PEFC. This results in a larger CSA than is necessary.
Spin - I was thinking about this myself but cannot find a graph in Appx 3 for a BS 1361 fuse. Am I going nuts?
PP