Hi guys,


I have brain freeze and need some help!


I'm currently looking to run in a radial socket outlet circuit to a bedroom from a spare way in the consumer unit. The total circuit length will be approx 10 meters of 2.5 t&e. The supply is a TNC-S arrangement with a Ze of 0.13ohm (by direct measurement). The circuit protection is by way of a 20amp Type B BSEN60898 mini circuit breaker. NO RCD!!


Normally I would just follow the typical values in the OSG. This time though, I decided to just calculate it... Have to keep doing it once in a while or I'll forget!! :-/
The cable itself is fine (obviously) until I check the cpc size using the adiabatic equation. Can someone tell me if I've got this right? :-/


Ze = 0.13


R1+ R2 = 0.23 (adjusted for temperature @ 10 x 19.51 x 1.2)


Zs = Ze + R1 + R2
= 0.36


230/0.36
= 639A


K factor = 115
Assuming instantaneous time of 0.1sec


S = sroot(639*x0.1)/K
= 1.76??


Thanks in advance! :)
 
looks like youre gonna need a cable with at least a 1.75mm cpc , which will be 6mm t&e ;-)


or maybe look at time current graphs for a 20a mcb ............


which will probably end up giving you a min cpc size of around half that.
 
Lets end this now, a 2.5mm2 cable to a socket as a single radial to a bedroom 10 mtrs away from the dist board?? yes okay get on with it, 16 amp mcb and you will be fine, fluck the calculations on this occassion.
 

Reply to Adiabatic question in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
841

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
254

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top