since when did the adiabitic account for main bond sizes......
Allready aknowleged
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Adibatic equation for 6mm earth in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
since when did the adiabitic account for main bond sizes......
Hi mate.
Think you might have been mis-informed there. No calculation is needed for main equipotential bonding conductors just select from the relaevant table in ol' red. 10mm earth is the smallest size to use upto 35mm tails, then 16, 25, 35 and 50mm. The largest size you would ever need to go upto for a bonding conductor is 50mm for tails of 150mm or over.
The adiabatic equation is only used to initially size/confirm the size of the main/circuit protective conductors.
Yes it was
It seemed appropriate
Only wish I could type so proficiently
I would be interested in seeing that as well ?