Hi mate.

Think you might have been mis-informed there. No calculation is needed for main equipotential bonding conductors just select from the relaevant table in ol' red. 10mm earth is the smallest size to use upto 35mm tails, then 16, 25, 35 and 50mm. The largest size you would ever need to go upto for a bonding conductor is 50mm for tails of 150mm or over.

The adiabatic equation is only used to initially size/confirm the size of the main/circuit protective conductors.


The IEE regs specify the size of main bonding conductors for NEW installations - if you were (for e.g.) carrying out a PIR on an installation, the adiabatic equation can be used to ascertain if the EXISTING bonding is adequate for it`s intended pupose, it may not be necessary to upgrade it unless further load/new circuit(s) are to be added.
 
I would be interested in seeing that as well ?

Based on your prospective fault current and the size of the main fuse, it is feasible for a bonding conductor of 6mm squared to be adequate to carry the full fault current of the installation up to the point that the main fuse blows WITHOUT DAMAGE. Clearly this is only appropriate on existing installations as the OSG now tells us what we should do without us having to use our brains.:rolleyes:
 

Reply to Adibatic equation for 6mm earth in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
250
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
723
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
695

Similar threads

  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top