just a quick one why do we use the adiabatic calculation for your main earth to your consumer when for me by the time youve done the calculation you could of thrown a 16mm earth in as its right next to your consumer
Because not everyone does just domestic. Try doing that in a 50,000sq ft manufacturing plant.
also...... you might have a 16mm main earthing conductor, but the main bonding conductor/s size is reckoned to be 1/2 of trhe minimum required for the main, so if the adiabatic says 10mm is OK for the main, 6mm is ok for the bonding ( unless it's TNC-S)
Reply to Adiiabatic question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...