I have it on a PDF......too large to upload here though.

PM me your e-mail if you like and I'll send it on.
 
Re: Adiabatic

Please confirm my calcs and methods, am calculating to confirm correct selection of csa for cpc

Line and neutral csa is 2.5mm^2 and csa of cpc is 1.5mm^2
Singles in conduit from a Eaton MBH120. This is a 20A MCB rated for short circuit current of 10kA.
Zs has been measured at 0.24ohms on 230V nominal supply.
Assuming k=143 and looking for disconnection time of 0.1s

Using the adiabatic S=sqrt(I^2t)/k and calculating from the above measured values:
PEFC = 230/0.24 = 958A
S = sqrt(958^2 * 0.1)/143 = 2.118 which indicates required csa of cpc = 2.5mm^2

Now using manufacturers data from tables provided:
PSSC = 10kA (because mcb is rated for this)
According to tables for 20A mcb with PSSC of 10kA the I^2t value is 33000
S = sqrt(33000)/143 = 1.27 which indicates required csa of cpc = 1.5mm^2

So is the use of 1.5mm^2 for the cpc correct?
 
Manufacturers data can always be used.

Indeed when I did my 2400 we were encouraged to look it up and use their figures as it makes for a more economical design (only after we had done all the adiabatics though):rolleyes:
 

Reply to Adiobatic in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
768
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

I have a Hoover HBCP3150, integrated fridge freezer. Probably 3 years old. It's immaculately clean inside and out. It looks brand new but the...
Replies
0
Views
330
Good question now to start with thermosetting insulated conductors are not tri-rated that is something different. Table 4E1A deals with this type...
Replies
1
Views
280

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top