Advice about PHEV car charging.
We have 2 PHEV vehicles in the family which we charge overnight in the garage, each car plugs into a normal 3 pin household socket. There is a small garage Hager consumer unit in the garage which has a 16A MCB protecting all the wall sockets which are wired with 2.5mm cable. The car chargers are 2.4kw with a current max rating of 10A. One night the 16A MCB tripped but we're unsure why.
My question is: Could the reason be that with both cars charging at the same time on the same circuit that it was being overloaded? If so could I safely replace the 16A MCB with a 20A or 32A MCB without causing any other problems.
Also the cable which supplies the power to the garage from the house is protected with 16A MCB, would I need to upgrade that also?
The circuit breakers are there to protect the cable it supplies. So you can’t just go uprating the breakers without checking the size of cable.
The way cable is run is also a factor. Clipped direct in free air can take more amps than buried in insulation, and the circuit breaker size will be determined from that.
Rule of thumb, 2.4kW / 240V is 10A each… so if both decided to charge at same time, that’s 20A pushing the 16A breaker.
At 2.5mm cable, you might be able to use a 20A breaker, but not 32, as that would be above the capacity of the cable. (Unless the sockets are wired in a ring, but there’s no info on that)
What size is the cable feeding the garage board?
A 16A supply suggests not very big.
Any spare ways in the Garage Consumer Unit?
I suspect you have a radial but whatever you could create two 16A radial circuits (providing you have a spare way)
As littlespark said you can't just upgrade the MCB to 20A for a number of reasons as well as it not being enough anyway.
I suspect the 2 cars would be plugged in on different sides of the garage so arrange the radials in that configuration. You don't want to inadvertently plug 2 in on the same radial.
You will also need to upgrade the cable and MCB supplying the garage to 32A.
You don't have selectivity in your current set up anyway with a 16A MCB backing up a 16A MCB.
Cable sizes for this would be dependant on length and installation method and volt drop. Also some consideration to the existing installation.
If you don't have a spare way then you could either get a larger consumer unit or upgrade the garage supply to 40A so you can have one 25A Ring. If your garage is wired as a radial with 2.5mm you would need to convert it to a ring or rewire in 4mm as 25A is right on the edge for 2.5mm as a radial. Best case scenario it can take 27A but that is dependant on a number of factors.
The above is a rough guidance on what you could do it would obviously depend on your current set up what would be best.
Another consideration is that normal 13A sockets don't do well having high loads connected for long periods, there are now dedicated ev charging sockets for this.
Hi littlespark,
All the sockets in the garage are wired from the same 16A MCB, not sure if that means it's wired in a ring?
The cable feeding the garage board goes underground from the house to the detached garage. All I can say about that is that it's a very thick black armoured cable. There's no information on the cable itself that tells me what the specs of the cable are.
Yes the 2 cars are plugged in on different sides of the garage. When you talk about a spare way I assume you're asking if there's a space in the consumer unit for another 16A MCB? If so, unfortunately there isn't.
Can you post a photo showing the big thick black armoured cable and the garage board?
We could maybe judge the size from visuals only.
Armoured usually has the size moulded into the plastic at regular distances… ie “3G2.5” would be a 3 core, 2.5mm
If it’s possible to uprate the breaker supplying the garage, it would give some more options.
Many thanks. 👍
Yes, I’ll do that tomorrow
There is some lettering embossed on the armoured cable but I can’t quite make out what it says. IMG_0514.jpegIMG_0515.jpegIMG_0517.jpegIMG_0518.jpeg
Hi,
I’ve sent the pictures you requested. I’m new to this sight so hope I’ve done it right. Many thanks for your help anyway 👍
No problem.
It doesn’t look like a big cable, to be honest…. So upping the supply to the garage may not be possible.
Do the cars have any programmable features as to when they can be charged? Time them so they charge at different times.
I understand you only have the charging leads with a 13A plug on them, and not a dedicated charge point that would have these smart features built in.
No problem.
Many thanks for your help littlespark.
It appears that there isn't an easy solution to the problem so I guess we'll just have to stagger the charging, probably charge each car on alternate nights. I don't think there's enough time to fully charge both cars alternately on the same night rate which is from midnight to 7am.
Thanks again
Being both PHEV, do they need much charging? I mean, they are hybrids rather than fully electric.
My mother in laws Volvo is a petrol hybrid, but at most she only gets about 20 miles on a charge... Which is fine for nipping down the town.
They asked me to fit a 32A charge point in case they ever go full electric in the future.
My wife’s Evoque gets about 32 miles on a full charge and I get about 28 miles on my F-Pace. I don’t know how long a full charge takes but I believe each one takes a few hours. I suppose I could charge each car for 3 1/2hrs to see how far they charge up. I’ll try that.
Indyisme,