I generally install them in dwellings, I do give the customers the choice though, but honestly though if you tell them there have been rumours of insurance companys are using surges to get out of paying for damaged electrical equipment they usually just tell you to put them in.

If they dont want it, just get them to sign a letter, just take a copy and attach it to your EIC.
 
443.4 refers and uses the term ‘shall be installed’. Basically if the installation has electrical equipment over the value of about £200 BS 7671 states SPDs shall be installed.
To paraphrase (without getting BS7671 out for exact wording), the requirement is essentially that where the value of equipment warrants it an SPD should be fitted. (This would require discussion with the Client.) It does not necessarily mean that where the value of the equipment exceeds the cost of installing an SPD that it must be done. I don't believe that is what is intended by the wording.
 
443.4 refers and uses the term ‘shall be installed’. Basically if the installation has electrical equipment over the value of about £200 BS 7671 states SPDs shall be installed.
To paraphrase (without getting BS7671 out for exact wording), the requirement is essentially that where the value of equipment warrants it an SPD should be fitted. (This would require discussion with the Client.) It does not necessarily mean that where the value of the equipment exceeds the cost of installing an SPD that it must be done. I don't believe that is what is intended by the wording.
 
I spoke to the NAPIT inspector today about this issue and he suggested that on a dwelling if it is overhead cable or has a lightening conductor you should insist on fitting SPDs otherwise offer it to the customer and if they refuse the extra cost just write it up on the cert.
BTW I'm new here though, unfortunately, I'm not new to the electrical industry and have had my own business for 34 years. I passed my 18th edition way back in august with 92% and I received the same advise on the course.
I'm just in the process of changing registration from the NIC to NAPIT and it's doing my crust in.
 

Reply to Advice needed On 18th edition boards. When do fit SPD boards? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
704
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
Yea I do It was more the spd at solar end I was more enquiring about than rcbo just wanted to confirm it for my own sake as I was questioning...
Replies
4
Views
651
  • Question
The ads are a temporary glitch, hopefully.
    • Like
2
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top