scenario: old kitchen being replaced

cooker circuit protected by (i think) a 30A rewirable fuse

6mm T&E going from DB the the 45A dp cooker switch

2.5mm T&E cable then goes from cooker switch to a double socket plugged into which will be the plug for the cooker and plug for the gas hob's starter.

new cooker says to use a 13A plug, however the manufacturers flex on the cooker is 3x1.5mm cable which is bigger than expected.

the question is ... is the 2.5mm T&E from the cooker switch to the socket big enough or does it need to be 6mm?

[FONT=verdana, geneva, lucida, lucida grande, arial, helvetica, sans-serif]wasn't able to ascertain the max kW the new oven will use however if the manufacturer is happy with a 13A fuse in the plug then i guess its not going to draw any current higher than 13A so the 2.5mm T&E will be fine?[/FONT]

thanks
 
13 a is fine, just remember to down grade the fuse

that fine just wanted to know if the 2.5mm T&E from switch to socket was suitable

im an electrical engineer in a different aspect, as opposed to a domestic spark but obviously ive done the odd job here and there, but never had to deal with cable selection so wanted a bit of advice on it.

as for downgrading the fuse - so i need to change the 30A rewirable fuse at the DB for a smaller one? is there a quick formula to work that out or should i be consulting the regs book?
 
think what he meant was that the 30A fuse is too high a rating to adequately protect the 2.5mm, although it's fine for the 6mm. a 20A fuse would probably be more appropriate.
 
think what he meant was that the 30A fuse is too high a rating to adequately protect the 2.5mm, although it's fine for the 6mm. a 20A fuse would probably be more appropriate.

thought it'd be that, nice one thanks puts my mind at rest, thought the wall would have to ripped into to change the cable to a 6mm T&E!

think most of these new cookers have 13A plus and run fine on 2.5mm now from what ive seen recently mind.
 
If the spur for the socket is less than 3m you dont have the fuse it down BUT most of us on here would reduce the main MCB to a 20A for a 13A plug in cooker with a spurred socket. Thats what I/we would do. Very simple resolve to your question but if you dont deal with this type of thing you just dont know.
 
If the spur for the socket is less than 3m you dont have the fuse it down BUT most of us on here would reduce the main MCB to a 20A for a 13A plug in cooker with a spurred socket. Thats what I/we would do. Very simple resolve to your question but if you dont deal with this type of thing you just dont know.

right nice one. my mate who is a spark mentioned the 45A cooker switch might effect my cable selection but i didnt know what he was on about as that just means the switch can handle that load correct? not as if its a trip switch. the main issues are MCB size(going to be 20A) , cable size (2.5mm), and plug fuse size(13A as per manufacturer). so the 45A cooker switch doesnt effect anything.

cheers for the advice, i know people dont like giving advice to non sparks but as i say im an electrical engineer, got my 17th edition, PAT and 2395 inspection & testing certs aswell, so im not just a bus driver trying my hand with electricity! just doing a job as a favour always good to get a bit of help from the pros.
 
right nice one. my mate who is a spark mentioned the 45A cooker switch might effect my cable selection but i didnt know what he was on about (yep, he dose not know what he is on about) as that just means the switch can handle that load correct? (correct) not as if its a trip switch. the main issues are MCB size(going to be 20A) , cable size (2.5mm), and plug fuse size(13A as per manufacturer). so the 45A cooker switch doesnt effect anything. (the cooker switch dose not effect anything unless you apply another 2 phases to it and switch it on and off 5 times in a row at which stage you can transport yourself in time........... ok the time travel is B.S. and so is your mates advice.)

cheers for the advice, (thank you) i know people dont like giving advice to non sparks but as i say im an electrical engineer, got my 17th edition, PAT and 2395 inspection & testing certs aswell, so im not just a bus driver trying my hand with electricity! just doing a job as a favour always good to get a bit of help from the pros.

Who the hell is the Pro that you have had advice from?????? Good luck with it and any problems gt back to us.
 

Reply to Advice needed on cooker circuit cable selection in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
551
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
991
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
922

Similar threads

Generally it would depend on the circumstances whether the armour is earthed both ends or not, and not just dependent on whether it's 2 or 3 core...
Replies
9
Views
354
  • Question
Thanks for replying
2
Replies
23
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top