Advice on generator earthing | Page 2 | on ElectriciansForums

Discuss Advice on generator earthing in the Talk Electrician area at ElectriciansForums.net

Sorry, I do not know what a “earthed centre tapped output” is, however I still struggle to understand how this will affect the installation as the generator earthing stops at the Ceeform connector into the installation, and from there, it is only the live and neutral of the generator that continue into the installation, the neutral being split to provide an earth before the consumer unit.

Actually, thinking about “earthed centre tapped output” this morning (a slow week for work) I suspect this may be what I have read about known as “V-O-V” generators, and those should not be used for domestic standby or similar installations. My understanding is that in V-O-V generators, the neutral actually has potential, and is NOT tied to 0v like a normal star point. If that is the case, then regular RCD’s will not work and the installation will not be suitably protected.
I would think an inverter generator will not have this output configuration, but I do not know if AVR output generators may still be V-O-V. I believe the clients need to confirm in writing that the wiring of the generator they buy is not a V-O-V configuration before purchase.
 

Reply to Advice on generator earthing in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
499
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
973
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
907

Similar threads

  • Question
Better/Smart/intelligent/expensive generators require two earth spikes set ~10-15m apart. They check the resistance between spikes and will...
Replies
5
Views
1K
Every oil boiler I've worked on has used a photocell for flame detection. Even though your boiler is inefficient by current standards, as long as...
Replies
4
Views
400

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top