Hi Folks,

If I'm extending a lighting circuit, (adding two pendants and an outside light) from an existing pendant but the board doesn't have any protection (an old BS3036 fuse board) What's the best way to add RCD protection?

The new cable for the switches can't buried more tore than 50mm deep and I don't want to whack an RCD FCU anywhere as they are quite bulky.

What would be the best course of action to take to install this circuit so it complies with the Regs?

Thanks,
T
 
Be interesting if any of them will commit what they have said to writing.

Wouldn't it just. Last time I checked I hadn't received an email.

The long and short of it is that NAPIT technical still consider RCD spurs and socket outlets to be acceptable but the guy I spoke to would not commit that to writing as 'it is just an interpretation of the regs'.

Here's where I have a problem with his interpretation. He quoted the part I've highlighted in red:-

531.3.6 RCDs for additional protection
The use of RCDs with a rated residual operating current not exceeding 30 mA is recognized as additional protection in compliance with Regulation 415.1. These RCDs shall be provided to comply with the requirements of Regulation 411.3.3.

RCDs for additional protection in AC installations shall comply with:
- BS EN 61008 series, or
- BS EN 61009 series, or
- BS EN 62423.

Where installed at the origin of a final circuit or a group of final circuits, an RCD with a rated residual current not exceeding 30 mA may provide fault protection and additional protection simultaneously.

NOTE: Consideration shall be given to the division of the installation (see Regulations 531.3.2 and 314.2).

And how he quoted it was that this specification of standards only applies when the device is to be installed at the origin. My interpretation of that segment means only that it can, in the case of high EFLI be used to provide fault protection when installed at the origin.

I did challenge him on this and basically said I thought he was stretching a bit, but that was his interpretation of the regs.

So, on the phone it's OK to continue using RCD spurs and sockets that are manufactured to BS 7288 but ask them for it in writing and it's a big fat NO!
 
@SparkyChick

The section you've highlighted in red is precluding to using an RCD as fault protection in situations where the Ze or Ra of an installation means it would be impossible to meet disconnection times otherwise. I.e TT or generator fed installations.

Or that's how I would interpret it.

The section just above that is pretty cut and dry in what is and by means of absence what isn't, suitable for additional protection.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Kent

Thread Information

Title
Advice on Installation
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
79
Unsolved
--

Advert

Thread statistics

Created
Thomas Connolly,
Last reply from
Bobster,
Replies
79
Views
8,673

Advert

Back
Top